How will I know that how many batteries I should connect to
my UPS unit?
Answer Posted / shamim ahmed
You Should Know the KVA rating of your UPS, time you want
to get Back-up & the Battery input voltage of your UPS.If
your UPS rating is X , time T and the UPS input voltage is
V then the Battery current capacity is:
I=X*T*1.25/V*0.7 AHr
suppose battery input voltage of your UPS is 36V and you
find the Battery capacity from calculation is 300Ahr.
then you can use 3pcs 12V 300AHr battery in series or you
can use 2pcs 36V 150AHr battery in parallel.
Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
What does bode plots shows?
Which are resistive loads & which one are inductive loads : Refrigerator, Split air conditioner, ceiling fans, well pump, fluoresecent bulbs, T.V, CRT Monitors, Adsl Routers, C.P.U, Printers, Deep Freezers, Speakers, DVD Players, Microwave oven etc. ? Output Power for these Appliances Would be same like this : P = V * A * P.F Or would be changed ? thanks
what is positive , negative & zero equivalent system resistance
What should be the magnetic balance test values for a 3 phase delta/star connected single primary dual secondary winding transformer (90 MVA / 2 X 45 MVA TRANSFORMER)
what is meant by surge? what we called for high currents?
i m electrical diploma holder i want to do plc $ Scada some body tell me which insitute is best for me near chandigarh
Draw the circuit of clapp oscillator?
The shot circuit in any winding of transformer result? Explain
what happens when series resonance occurs?
How to calculate the phase to phase clearness of HT /// LT bus bar?????
3 phase induction motor connection star or delta while using ac drive motor is .75 to 5.5 kw
how pt is using
What is effect of harmonic current (Draw by VFD) on power system/ electrical Equipments ?
How to calculate the sag of OPGW during stringing???
What will happend if given Vfd out put to step up transformer