IF we have 500kva transformer 11.0/0.415V, 50Hz. How to
calculate the current on HT & LT side, how can we consider
for its breaker (HT & LT both)? You are requested to solve
the question herewith.
Answers were Sorted based on User's Feedback
Answer / antaratara ghosh
current on HV side= 500/(1.732*11)
= 26.24 A
current on LV side= 500/(1.732*0.415)
= 695.6 A
Breaker on HV side will be 630 A VCB (since it is the
lowest available VCB and in HV side you have to go for
VCB/SF6)
Breaker on LV side will be =greater than (1.2*695.6)A i.e.
834.72 A
so we consider it to be 1000 A ACB
| Is This Answer Correct ? | 19 Yes | 3 No |
Answer / a.i.a
As, usually the ultimate load current for any distribution system take 20% spare loads for future , so full load current shall be multiplied by 0.2 more (i.e 1.2) to calculated MCCB rating.
hope you got the correct answer.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is Ten Delta Test ?
is starting current of induction is high or stating current of ransformor is hign ,for the same rating
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
What is stepper motor. What is its uses?
why generator is star connected ?
where we use zero sequence current transformer or core balancing ct.
how the length effects the ampacity of the cable? if a cable is carrying a current of 100A for 50m length then what will the effect on current if we double the length?
What is HVAC, PLS SEND DETAIL OF hvac.
How to design a Unit auxiliary transformer for a power house having a unit of 65 MW and Generating voltage of 11 KV and Secondary voltage of 433V
how to calculate Amp, 2 different Amp of batteries? Example: No. of Batteries = 2 Battery voltage = 12V 1st Battery rating = 17AH 2nd battery rating = 30AH between parallel connection then output volt 12v Amp?
What is corona loss?
what is the purpose of checking IR and Megger values in motor windings?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)