Answer / rajkumar nirmalkar
We provide earthing to restrict the fault current since the
earth is considered to be as zero potential .
We also protect man and machine from the hazardous current
flowing from the equipment in case of any fault.
| Is This Answer Correct ? | 27 Yes | 4 No |
Answer / baiju k nair
It is nothing but a protection for the personnel and the
costly equipment. In case of any falut in the system a
large amount of current flows through the equipment which
may damage the costly windings of the motors or
transformers, and can also be dangerous for the personnel
at sight so earthing will divert the large current to the
earth thus protecting the equipment and the personnel.
| Is This Answer Correct ? | 19 Yes | 4 No |
Answer / sujit288
It is the connection between the metalic body of equipment
and mass of earth for protect man and machine from the
hazardous current flowing from the equipment in case of any
fault
| Is This Answer Correct ? | 16 Yes | 6 No |
Answer / t.c.raghavendran prabhu (lnt)
There are three major Factors that influences good earthing:
1) Earthing is mainly done to arrest the flow of jumping
electrons from the body to the ground because the ground
potential is zero.
2) Mainly body earthing of the equipment has to be done to
avoid the damage and losses of machine & humans.
3) Good earthing resistance is 1-2 ohms.ELCB ie,Earth
Leakage Circuit Breaker has to be placed in the Panel
boards for the safety purposes.
| Is This Answer Correct ? | 6 Yes | 3 No |
The earth connection improves service continuity and avoids
damage to equipment and danger to human life.
The object of an earthing system is to provide as nearly as
possible a surface under and around a station a uniform
potential and as nearly zero or absolute earth potential as
possible.In general, all parts of apparatus other than live
parts,shall be at earth potential which is always at a zero
potential.
( This information is referred from IS:3043 - 1987 for the
benefit of readers ).
| Is This Answer Correct ? | 2 Yes | 0 No |
phase association of 3PH L&T static CT meter is wrong. means 1PH & 1 CT connected properly and other 2 voltage and CT's inter changed. what would be the impact in the reading?
What will Happened if the polarity of CT is changed?
Why 11KV/440V distribution supply use for Domestic use?
3 Answers Essar, Getco, Nissan,
what is the meaning of osr in transformer.
why motor rating in kw?
What are the common sources of energy?
Do you know the faults occurs generally in motors and how to rectify them?
if my load is not in continuous operation so what type of panel is required APFC or fixed capacitor bank without APFC whether C.T is required in both cases compulsory? explain detail
Determine a suitable number of slors and conductors per slot for the starter 1 winding of a 3 phase, 3300 V. SO Hz 300 rpm alternator. The diameter is 2.3 m
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
what's ripple content in rectifier? how it formed?
how to calculate the megger values for motors and cables?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)