phase association of 3PH L&T static CT meter is wrong.
means 1PH & 1 CT connected properly and other 2 voltage and
CT's inter changed. what would be the impact in the reading?
Answers were Sorted based on User's Feedback
Answer / manjunath tc
Phase angle error will come into picture and meter will record slow.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shankar
Lets us understand this problem by taking load as constant and the incoming supply initially it was RYB in sequence.
let Vr=10<0 Ir=5<-10
Vb=10<-120 Ib=10<-20
Vc=10<-240 Ic=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-140)+VbIbcos(-250).
=41.5 watts.
Now lets us consider Y and B phases were wrongly connected to each other
Vr=10<0 Ir=5<-10
Vy=10<-240 Iy=10<-20
Vb=10<-120 Ib=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-240)+VbIbcos(-130).
=3.781 watts
so the energy meter will records less units
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / surendar
if 415 v is appliex at three phase in your situationi f r phase is right it will get
higher vol. and other two get lower vol....right ans should be all the three
sholud b same
Is This Answer Correct ? | 2 Yes | 4 No |
electromechanical relay type identification example : type=tjmh t-stants for j- m- h-
what happens when we apply dc to a transformer
what is the transformer efficiency?
If DG runing time neutral is disconnected what will be the effect in Engine and Electricial panel.
WHAT WOULD BE THE FORMULA OF WIRE GAUGE FOR A FULL LOAD CURRENT
solar cell voltage?
Explain the function of VFD
Give some differences between open loop and closed loop control systems.
can u tell the difference between star - star transformer and delta to delta transformer?
Which state of India had first started power reforms?
sir pls tell me . our ct specifications are 120/5 ,2 core , 0.2 and 5p10 class , 30va and 30va buden. insted of 30 va i want use 15 va. can i use?
How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?