What will Happened if the polarity of CT is changed?
Answers were Sorted based on User's Feedback
Answer / jk
Dear MMK. What's wrong UR posting. Ammeter reading from
left to right(0 to 90DEgree). It's starting point is
leftside only. then how it possible.
I think, for messuring CT it may work. but in
cause of protection CT, defenitly it will cause for
tripping the relay & system
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / k.prakashchandra
Only the meters which require voltage input also show the
negative readings.Directional and distance relays(on reverse
zone) trip.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / sanjay sharma
It is depend on type of scheme, in protection , if three phase ckt then reversal of 1 CT polarity relay will (if set value Reach), reversal of all three phases will not effect for normal protection (except to directional protection). In case of metering Ameter will not effect, but energy meter will not work,if single CT reverse in case of three phase, mode (import/export) will change.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / chadu
CT refferce to current transformer to sence the current.
if u reverse the ct treminals ur the same current reading
but with opposite polararity.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / aggarwala111
Ammeter show the opposite reading as previous.
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / grg
If we reverse the polarity the relay will see reverse
direction.The protected zone will get reversed.(incase of
distance protection)
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / sanj
CT polarity is vital part. if polarity changes of any ct out of 3 impact will be there both for measuring and protection ckt.
For measuring ckt please watch
https://www.youtube.com/watch?v=FqLVEeoaXws&t=181s
and for protection ckt impact watch
https://www.youtube.com/watch?v=p-cuvTe8sX8&t=129s
| Is This Answer Correct ? | 0 Yes | 0 No |
how electricity is generated an supplied till consumer
How to test the vector group of a Yd11 transformer? what are the relations to be checked between various vectors to confirm this vector group?
Why does the radius of armature is less than the radius of pole shoe?
Why? We r used 50sq. mm. And above size cable in 3.5 core and below size are used in 4core
if we use contactor & MCCB both in a feeder.in this feeder rating of contactor is higher or lower or same of MCCB rating & why?
Two bulbs of 500w and 200w rated at 250 v will have resistance ratio as ?
2 Answers CGL, Dreamz Infra, Sunny Developers,
What is Skin effect of the cable?
1.type of oil in used in transformer.
What is the type of earth fault protection used in battery? explain.
whats the necessary to correct the power factor using capacitive banks in industries?
i) in which cases should we go for neutral and where should we go for ground? ii) in domestic supply we are getting 230v a.c.and what is the amount of current?
For what purpose and why ACBs are used
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)