how to calculate the megger values for motors and cables?
Answers were Sorted based on User's Feedback
Answer / murali
thumb rule 1KV we get 1Mohm. if suppose 415V motor we get 0.45Mohm.
Megger is the instrument name. it is insulation resistance value.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / pradyumna171
megger value of any appleance should be 2 multiply with working voltage in kv plus 1 ie a 440 volt motor should have 1.88Mohm (2* .440 +1) , it is the minimum value. And megger voltage should be twice of working voltage of appleance.
Is This Answer Correct ? | 2 Yes | 1 No |
WE HAVE THE DC RECTIFIER 1500A, INPUT VOLTAGE IS 3 PHASE. HOW TO CALICULATE THE LOAD? 3 PHASE SIDE EITHER dC SIDE. PLEASE SUGGEST ME
Hi My Dear All Friends, There is one question it is widely used in Power Project's High Voltage Engineering. Question- What is the diffrence between Earth fault and Back up Earth Fault....???? . . . . . . Have A Good Day
Explain cos(theta) and Sin(theta)
What do you mean by Transformer?
9 Answers Hyundai, NTPC, wbsedcl,
how fault in an electric system is detected & hw protection of equipments is done ?
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
please tell me the all the spcications of the 100MW 11KV HYDEL POWER PLANT SPECICATIONS
What is the need for checking knee point voltage for CT's?
What is broken wire condition in transmission line?
What is communication? What are the different stagesin the communication process?
Can RCD's used to protect the VVVF drive if not why.
when we r using 3.5 cable for a bldg. and put laod on each phase using the neutral and neutral is the return paht for the phase so the current of the neutral must be Ir+Ib+iY (return).But the size of the netural is .5 as comper to the phase.