Answer / rabi
Neutral- it is a point where the sum of the current meeting
at that point is zero. E.g. in three phase star connected
winding the neutral is the point where all winding is
meeting at a same point obviously at normal operating
condition.
Ground- ground and earth both are same term. it may be a
reference point for in an electrical circuit from which
other voltages are measured, or a common return path for
electric current, or a direct physical connection to the
Earth.
Earthing -it is nothing but the process of connecting all
the neutral points of the equipment and non-conductive
exposed part of the metal structure to earth.
| Is This Answer Correct ? | 141 Yes | 19 No |
Answer / kalidassallinterview
Earthing : To connect the machinery body to ground by a
conductor it is called earthing.
Ground : Ground is a one terminal, it having zero volts.
Neutral: The junction of 3phase. In balanced condition this
voltage is zero.
kd
9840159504
| Is This Answer Correct ? | 29 Yes | 17 No |
Answer / jaymin shah
Earthing: to protect from shock we have toe earth all the equipement and ins. Include AC,socket
Ground: to protect equipement body we have to ground it..
Neutral: it is completing the ckt.
| Is This Answer Correct ? | 19 Yes | 10 No |
Answer / harshad pingle
Neutral= 0=In=Ir+Iy+Ib i.e summation of three currents
equals to the neutral current which is zero.
Grounding= Zero potential point. It may be the floating
neutral of star connected system.
Earthing= The system connected to earth where the system
max leakage current can flow.
| Is This Answer Correct ? | 14 Yes | 7 No |
Answer / sendhur
Ground and earth are one in the same, and don't normally
carry any current - they are "reference" ground.
Neutral is the grounded side of an AC outlet. It carrys
current, it is the return path for AC. Although it is
grounded at the utility pole, it should not be grounded
anywhere e
| Is This Answer Correct ? | 15 Yes | 10 No |
Answer / baig shahabaj
EARTHING: it is defined as connecting the metal body or non current carrying part of electrical installation to solid mass of earth
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / rehan khan
in Earthing system we connect the system with the earth pysically for the sake of safety . while ground is not physically connected to earth but is a reference potential point and return flow path for currrent from different parts of circuit.........
| Is This Answer Correct ? | 12 Yes | 9 No |
Answer / pankaj agarwal
earthing means neutral earthing. it is connecting the
current carrying points in the circuit to earth. this is
done for the purpose of operation of earth fault relays.
grounding means equipment earthing. it is connecting tha
non current carrying parts, like metallic enclosure, to the
earth. this is done for personnel safety.
neutral is a common return path in a multi phase circuit,
generally earthed to provide a reference voltage.
| Is This Answer Correct ? | 29 Yes | 28 No |
Answer / annasaheb n shinde
1.NATURAL- winding is star connected & voltage this candition zero.
2.ground- electrical units shefty by voltage current case
| Is This Answer Correct ? | 4 Yes | 7 No |
can we use existing 6300V alternator for generating 6600V by increasing excitation,what are advantages & disadvantages to alternator & motors of 6600V.
what is difference between co-generation and captive power plant?
How select ELCB for 32amp. socket having quantity 12Nos. We have to do this wiring in PLANT. Please Also explain the incoming cable specification.
0 Answers Gulf Industrial Services Company GISCO,
what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks
What is industrial automation ??????
how to increase or decrease speed in DC shunt motor by DC convertor
in cvt,there are two windings,1a,1n and 2a,2n.in my one project i use only one winding i.e.1a,1n. the other winding is not in use, so i connect it in open delta and want to close it by ibsertibg thermal resistor. the output of cvt is 132kv/115/sqrt3. plesae tell me exact value of resistor, so i may close it to avoid the resonance phenomenin. send me answer on this email adress please. aetcon-po@aetcon.com
why one pin of plug pin is longer than other two? In some mobile chargers one pin is made not conducting .Why?
working function importance of mdc meter
I'm looking for a softcopy manual set for a Credence ASL- 3000. Anyone know where I can get it?
CAN ANYBODY EXPLAIN WHAT ACTUALLY MEAN BY THE PHASE DEFFRENCE? R,L,C CIRCUITS?
when we start the tube light, then it takes initially 1100 volt, after glow it takes 120 volt?(when we give 220 volt a.c.)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)