What is the basic difference between earthing, ground and
neutral?
Answer Posted / rabi
Neutral- it is a point where the sum of the current meeting
at that point is zero. E.g. in three phase star connected
winding the neutral is the point where all winding is
meeting at a same point obviously at normal operating
condition.
Ground- ground and earth both are same term. it may be a
reference point for in an electrical circuit from which
other voltages are measured, or a common return path for
electric current, or a direct physical connection to the
Earth.
Earthing -it is nothing but the process of connecting all
the neutral points of the equipment and non-conductive
exposed part of the metal structure to earth.
Is This Answer Correct ? | 141 Yes | 19 No |
Post New Answer View All Answers
Transformer how to maintaince a check b check c check d check
which VFD is better ( LT or HT)
I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?
Draw torque - speed curve and load curve of induction motor? mark operating point ?
What is the difference between Static and servo controlled voltage stablizer?
what type questions asked in hp cl
How much depth n width required for laying of 1X70 Sqmm Cable in Desert???
what is the difference between electrical and electronic choke?
what is servo motor and how to work it.
1.why are not using acb 33kv ht side? is there any problem 2.what is difference between acb,vcb,sf6 breackers? 3.what is the function of invertor and convertor in ups?
As you achieve greater success with the company after some years, Will you like to be a share holder in our company?
Dear Sir/Madam, I have one questions we have three steam turbines and one Gas turbine and our industry linked with the public network, we have protection system one of the protection is reverse power we can export just four MW only i would like to ask about how to calculate the reverse power. Thank you in advance best regards
What difference between ref protection and differential protection ?
While converting delta into star or star into delta ,the three values of resistances remains unchanged .Find out the value?Let In star R1=x;r2=x;R3=x On converting into delta,R12=x;R23=x;R31=x Find the value of x
i want to put single phase load on scott connected transformer,eventhough how to balance the transformer.