I have tow 200 KVA UPS, both are in parallel mode.My
question is that, both are running on battery when power
fail, if one of them fail (Eg rectifire fails or some other
reason), at thet time reverse power will come to faild ups
if it comes then it will harm to failed ups or not? if not
then how it protects to faied ups????????????????
Answer Posted / sathishkumar
hi you mean both the UPS in PRS(parallel redundancy systen)
mode.then u have to connect the battery back to each UPS
separately.untill unless we are using as single sourse we
should not connect the both possitive terminals of Battery
bank connection in a common bus bar.if any one UPS failed
and EB power also goes off the entire load will be shifted
to single UPS which is working good condition also the
Battery bank which belongs to that battery bank only
support to the load.
remember in PRS mode output only paraled not input sources
(AC mains and battery back up)
Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
State nyquist stability criterion.
DERIVE AN EXPREION FOR MAXIMUM POER TRANSMISSION, WHAT ARE ITS APPLICATIONS.
mention hazard experienced during installation
What is big transformer parts and their function ? Ty
Explain cmrr?
What is warm / cold start of HT motors. How many warm start & cold start are possible in a day?
please forward me the type of questions which would rise while me attending to 33KV Electrical License to my mail ID:vadrevu_raghava@yahoo.co.in
What are motor generator sets and explain the different ways the motor generator set can be used ?
In a 3 phase 4-wire system. For a 3.5 core cable if all loads are single phase and balanced, what will be neutral current? will it be sum of all phase currents? Or it will be zero? And if loads are unbalanced what will be neutral current?
Define resonant peak?
Dear Respected sir how to test ABB REX521 protection relay by relay tester.
Is there any Electrical supervisor license which gives permit to work whole India rather than individual state??
sir my exam is on 19/6/2013 under electrical branch pls send me sample aptitude questions as well as sample technical questions for jindal steel and power company
how we decide the require size is this for a known current at fuu load?
How can we calculate cable size in Low voltage & high voltage