how to connect generators in parallel and what are the
required equipment to do so?
Answers were Sorted based on User's Feedback
Answer / paramesh
for the two generators connected in parallel by following
conditions:
voltage of both machine will be same
frequency must be same
phase sequence must be same
the equipments are:voltmeter,ammeter,synchronuscope will be
used.
Is This Answer Correct ? | 20 Yes | 0 No |
Answer / bijulal
for the two generators connected in parallel the following
conditions:
voltage of both machine will be same
frequency must be same
phase sequence must be same
the equipments are:voltmeter,ammeter,wattmeter,
synchronuscope& reverse current relay will be
used.
Is This Answer Correct ? | 10 Yes | 3 No |
if any leas acid battery is having low or high sp.gravity taen what will be effect of battery and why
WHY EXCITER PHASE SEQUENCE ARE OPPOSITE THAN STATOR SUPPLY PHASE SEQUENCE IN SYNCHRONOUS MOTOR >
if 300 hrs not comleted at wat interval b.c,d checks og take place
What is PCCB?
my project load is 6 MW so please suggest the size of cable.. ALU 3c 400 aqmm cable can be sufficient.. is there any thumb rule for calculation of cable size please help me
iam completed my DEEE in eillm university. can i get the c licence in tamilnadu its possible or not
why one side of tubelight glows after switch off ?
how to find out three phase motr kw with out name plate..
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer
what is diff kav & kvarh?
what is formula for zero phase sequence of nuetal earthing transformer of 6.6 kv
draw a circuit diagram connecting transformer OLTC- RTCC- VCB-Marshalling Box otherwise Explain in words