Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


can we use metering current transformer as protection
current transformer if not why? & if yes why?

Answers were Sorted based on User's Feedback



can we use metering current transformer as protection current transformer if not why? & if yes..

Answer / arun

Selection of CT for protection is majorly depends on the
burden limit and Kneepoint voltage at which the core of the
CT gets saturated,after which it cannot produce the
tripping emf in its core.

So check the burden of CT and kneepoint voltage.

Is This Answer Correct ?    19 Yes 2 No

can we use metering current transformer as protection current transformer if not why? & if yes..

Answer / ranga

because protection CTS are rated for high currents than the
metering CTS, so we should not use metering CTs for
protection purpose.

Is This Answer Correct ?    17 Yes 9 No

can we use metering current transformer as protection current transformer if not why? & if yes..

Answer / felixraj

the only diff is the knee point voltage
in metering CT this value is very low, because of this
during fault condition the ct get saturated and o/p almost zero
(metering equipments are protected from fault surge)

protection miss leads in metering CT (it may fails or
nuisance tripping)

Is This Answer Correct ?    10 Yes 3 No

can we use metering current transformer as protection current transformer if not why? & if yes..

Answer / mohammad

Metering and protection CTs have different accurecy class
level as metering CT has 1 class level and for protection
itis represented by 5P,10P etc..

Is This Answer Correct ?    5 Yes 3 No

can we use metering current transformer as protection current transformer if not why? & if yes..

Answer / mohsen khoshsefat

Introduction to Protection Transformers
Protective Current Transformers are designed to measure the
actual currents in power systems and to produce
proportional currents in their secondary windings which are
isolated from the main power circuit. These replica
currents are used as inputs to protective relays which will
automatically isolate part of a power circuit In the event
of an abnormal or fault condition therein, yet permit other
parts of the plant to continue in operation.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What does quality factor depend on in resonance?

0 Answers  


what is tower earthing and what for it is required

1 Answers  


in thermal power plants by opening the turbine governor valve increase the generator load. how

3 Answers  


What is the unit of magnetic flux density?

0 Answers  


What is the major difference between cnc and plc. why cant we use plc instead of cnc

5 Answers  


how ELCB drip when earth and phase touch together?

2 Answers  


If a rotary UPS is in line through grid power; What would be the impact on Power Factor if the load through rotary ups is 25% , 50% , 75% & 100%. Will the power factor reduce with less load?

0 Answers  


When both contractor star & delta is hold in star delta motor ?? So what happen in this case ??

1 Answers  


Is there any Institution for giving M-tech in Electrical engineering for those who r in service? Give the details please.

0 Answers   CB&I Lummus,


how to select proper cable for ct wiring so that drop within the limit.

0 Answers  


How to confirm the Phase shifting Transformer VECTOR GROUP relation , as below ZNy11.45d10.45-ZNYy0.15d11.15

0 Answers  


Why the power factor of the alternator in power plant is kept .8 lagging. Can't we maintain it at 1.

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)