Why the power factor of the alternator in power plant is kept .8 lagging. Can't we maintain it at 1.
Answers were Sorted based on User's Feedback
Answer / sidharth
The pf is maintained at 0.8 because generator has to supply reactive power to the connected transmission line if pf is maintained at 1 then the distribution transformers would not be energized as it requires some reactive power for its core to produce magnetic flux.Also the due to line capacitance the receiving end voltages will get higher than the sending end voltages. For more reference consult reactive power control topic.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / lokeshraj
We use the capacitor bank to maintain the power factor at .8 when it goes below this value, capacitor compensate the reactive power needed, and improves the power factor. Why don't we use this much value of capacitor that the pf becomes unity. Because if we use the capacitor at the load end and makes the pf unity the losses in the line will be decreased and the load capacity of the line will be increased.
Only in unloaded or lightly loaded condition the receiving end voltage of the line becomes higher than the sending end voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
For transmitting power with low value of ferrenty effect .power generating station pf should kept 0.85 -0.80
| Is This Answer Correct ? | 0 Yes | 0 No |
what are the possible reaons & remedies if resistance of NGR getting heat up
What's difference between a400amps lt contactor and a400amps lt circuit breaker
Explain the construction of the conservator, operation and purpose, and draw the diagram of the conservator.
How many VSC based HVDC are there in India and the world
1. What are the tests to be carried out for CBCT? 2. can measure the secondary resistances? 3. with respect to secondary maximum how much voltage can be applied for IR test.
what is the function of DC panel in substation?
why we use end termination kit for ht xlpe cables
What is the previous name of Cox's Bazar
Sir, I need a power supply at 380V. The supply I get in three phase is rated 415V. The total supply I have from the supply company is 70KW. Kindly inform if it is better to use a voltage stabiliser for this purpose or a transformer
star delta advantage and disadvantage?
To attain a powerfactor more than .95, how much kvr should we use for 100 HP of current
4 Answers Bhel, Scooters India,
Is there a diode made that works with AC 120 volt 20 amp? If so can it completely stop all current flow in 1 direction at all times?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)