can we use metering current transformer as protection
current transformer if not why? & if yes why?
Answer Posted / felixraj
the only diff is the knee point voltage
in metering CT this value is very low, because of this
during fault condition the ct get saturated and o/p almost zero
(metering equipments are protected from fault surge)
protection miss leads in metering CT (it may fails or
nuisance tripping)
Is This Answer Correct ? | 10 Yes | 3 No |
Post New Answer View All Answers
What are the difference between CT/PT operated Meter and RRAMR Meter for HT/LT application?
sir,in our plant we r using SATEC PM172E power reading meeters in HT panel side it is monitoring the MB data smart viewer(sever).but last one week we did not get readings inthe server only available in meeter.tell me how communicate meter and server. and also what steps we take for checking.
current transformer balance the power level on both sides. e.g in case of step up, at secondary side voltage rise but current decrease and vice versa in case of step down transformer. but how this power level remains same in case of current transformer and voltage transformer
What are hrc fuses and where it is used?
if sf6 gas low in gis what will happen
Generator,motor and alternator Working principal Please explain easily
Do closed loop systems require manual input?
how to measure the current by compact digital equipment with dislay which fit inside any equipment
Is there any problem about which the drive (inverter) doesn't show/display the alarm and/or fault but instead of this , it doesn't work ? I want to know that could there be any kind of problem in the drive when the drive doesn't display the alarm and/or fault ?
how to calculate singlephase motor efficiency?
WHAT IS IEC? & WHAT IS BENEFIT TO PRODUCT FROM IEC?
WHat is the general checks required for Dry type transformers
Dear friends I want to design busbar for1600 kva transformer(i.e2100 amps) what are all the factors to be considered before selectinga busbar what are all the standard sizes of busbars what is the formula for finding current of copper and aluminium busbar
how to flameproof electrical motor on the shaft?
Explain what is clipper and clamper circuits?