in thermal power plants by opening the turbine governor
valve increase the generator load. how
Answers were Sorted based on User's Feedback
Answer / manuks
I assume that the machine we talk about is synchronized
with some power grid. In this case the machine will run at
the frequency of this grid. Any fluctuation on the part of
this machine will bring the synchronizing torque into play
and pull the machine back to synchronous speed. Now suppose
we are opening the governor valve to increase the machine
speed. The synchronous torque will immediately put more load
on the generator, to prevent it from speeding away. This
will result in an increase in its load. Any effort to
decrease the speed will result in the synch. torque removing
some load from the machine and again its speed wil remain
the same.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / arvind
first we will know why governor is used in power plant is
because to maintain frequency constant, in india it is 50hz
now by opening the turbine governor valve increase the
generator load because as you load increases, the frequency
will drop and it is the most impontant thing to maitain
frequency thats why it is done.
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mitesh
governor valve increase it that time generator load is
deincrease
| Is This Answer Correct ? | 3 Yes | 7 No |
What is given by the definition in BIL IMP/PF = 950/395 kV. This was found in a name plate of a power transformer.
what is level 2 automation?
In a 11kv/433v transformer,at the LT side ie 433 V side why do we need to put 3.5 core Cable upto Panel.The full load rated Amps is 666 at LV side.What value of current will flow through the Nuetral Conductor.Why can't we use 4Core Cable instea of that?
definition of fault level in powersystems?
voltage at generation stage is usually- ? a.11kv b.33kv c.66kv d.220kv
Hi, My plant daily consumption is calculated as 3.8MWH but my supplier has sanctioned an power of 2.6MW per day. how can i equal or distinguish this two factors
According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.
what is fuction static switch in ups and tell me use parts name and fucion
why the tapping of transformer on ht side??????
12 Answers CTS, OPTCL, Visa Steel,
what is intermediate switch
Explain Even and Odd signals?
Why use the VCB at High Transmission System ? Why can't use ACB? Pls explain the ans.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)