if we convert kw into kva,which one formula use by us,pls
tell me?
Answers were Sorted based on User's Feedback
Answer / mohammed hussain a
Power in KVA = (1.732 * V in Volts * I in Amps)/1000*PF
For 3 Phase Supply
Power in KVA = (V in Volts * I in Amps)/1000*PF For 1
Phase Supply
or
KVA = KW/PF
Is This Answer Correct ? | 34 Yes | 7 No |
Answer / r.muthu kumar
Killo Watts When KVA is knomw = KVA X Power Factor
Killo Watts 3 Phase = (I X V X 1.73 X P.F.) / 1000
Killo Watts 1 Phase = (I X V X P.F.) / 1000
Is This Answer Correct ? | 19 Yes | 3 No |
Answer / parvez ahmed
For 1KW=1.25KVA
So...
PF=.8
1KW
KVA=KW/PF
=1/.8
=1.25KVA
Is This Answer Correct ? | 15 Yes | 1 No |
Answer / kanth
actually
kw= vicos$
and
kva= vi
so KW= KVA/Cos$
cos$=KW/KVA
or
KVA=root of (Kw sq +KVAR sq)
Is This Answer Correct ? | 6 Yes | 1 No |
For 3phase supply
KW= 1.732VIcosQ
KVA=1.732VI
for 1phase supply
KW=VICosQ
KVA=VI
if KW givwn means
KVA=KW/CosQ
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ravinder
AS PER THE PRACTICAL ASPECTS CONSIDERING PF
PRACTICALLY ....FOR 50 HP MOTOR WE HAVE TO TAKE 37.5 KW
(I.E. FOR 100 HP WE ARE TAKING 75 KW)......
Is This Answer Correct ? | 1 Yes | 0 No |
What are the disadvantages of hydropower?
Why R ph of Hv and Lv is shorted or joined together while taking vector group?
Can we use generator transformer as step down transformer? How?
how to decide choke rating for drive?
what will happen if there is a voltage leakage or current leakage in an electrical train
what is the use of megger? and types
11 Answers TNEB Tamil Nadu Electricity Board,
how can we change the phase angle b/w two phase?
How can we select suitable capacity generator for three phase load (inductive load) and how to take study analysis in 3 three phase load system ?
how steam converted into electricity in power plant
Why collecting electrode of ESP to be earthed
how to calculate the ngr capacity(nutral grounding resistor)
inductance and capacitance may result in periodic reversals of the direction of energy flow,how???