Wht ar the reason for low voltage on consumer side?
Answers were Sorted based on User's Feedback
Answer / vinay gupta
A consumer may suffer from low voltage because of one or
more following reasons:
1.Due to power generation at low voltage at generating end.
2.Due to low power factor, bcoz of which more current to be
carried out for meeting the same load and hence line losses
increases which is responsible for the low voltage.
3.Due to over load.
4.The voltage drop across the conductor or cables is the
major cause of low voltage.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / mani
The low voltage mostly in the peak hours why because that
time more number of consumers are using the power.So the
voltage will get reduced on the distribution line.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / manjifera
its because of lagging power factor due to inductive load
e.g mixer grienders,motors,transformers. which dont have
capacitors to supress lagging current.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / lavanya
during power transmission at the grid there is low voltage
and high currents and when it passes through different
substations it step downs and at that time there is high
voltage and when it comes to house hold purposes there is
low voltage in this ohms law does not work
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / austin kpoto
The technical malfunctions and reason are many here are few
1. One possible cause should be main conductor load phsae
are over loader or cabe to consumer not the recommended
size.
2. In properely load balancing to pahses
3. Faults AVR output
4. loose conductor from main breaker box to consumer
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / rajeshsan
When the customer at load end is very long from the source. Due to voltage drop the customer located at very long will fall low voltage. Hence, the Electricity Board will install the service transformer at regular interval.
| Is This Answer Correct ? | 1 Yes | 3 No |
Explain the advantages and disadvantages of thermal power plant?
what is sevice settings for mccb?How can be it setted?
Can we install and run MCCB suitable for 440v 3Phase 4wire system, on a 220V 3Phase 4Wire System.
A 400KVA transformer has 400 Hz frequency. If the frequency is changed to 50 Hz, then what will be the new KVA rating?
why earth fault current is always less than the o/c
What are the raitings of Mcb,mccb and Acb in detail ??
when a primary current injection test is required, it is accomplished by what?
How the size of transformer decreases if we increases the frequency?
We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Suppose we have long 2 core DC cables running from our DCDB in control room to the load (length of around 2 to 3 km). Do we need to protect these long DC cables from earth leakages or not? If yes how?
what is draiv work
what is threshold voltage for a relay???what does it exactly means ?whats its value in our indian transmission system say 11kv feeder RMU relay
How induction stove works?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)