when a primary current injection test is required, it is
accomplished by what?

Answers were Sorted based on User's Feedback



when a primary current injection test is required, it is accomplished by what?..

Answer / mohammad farman khan-abu dhabi

Primary current injection test require at time of
commissioning to distrubution switchgear.High pot theory.

Is This Answer Correct ?    3 Yes 0 No

when a primary current injection test is required, it is accomplished by what?..

Answer / brijesh

Primary current injection test require at the time of
commissioning to the current transformer.

The purpose of it is to check the ratio of C.T.

and for checking of C.T. circuit.

The test is conduct by means of primary injection test set.
In test set there is a current transformer and variac.

Is This Answer Correct ?    2 Yes 0 No

when a primary current injection test is required, it is accomplished by what?..

Answer / arvind negi

Primary current injection test require at circuit
protection equipment throw.

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

how we can measure the dc current instead of clamp meter ?

1 Answers  


why transformer is rated in kva instead of kw?

1 Answers  


how can we calculate air compressure capacity

1 Answers  


What is electrical charger?

3 Answers   HCL,


Why does the power consumed is always constant even if a fan speed is altered?

5 Answers  






what is the min and max ohmic resistance for the earthing rod installed for lighting poles for street light network

1 Answers  


how does commutator convert a.c to d.c?

0 Answers   NRSC National Remote Sensing Centre, RBC,


what is the difference between servo voltage stabilizer and general voltage stabilizer?

1 Answers  


what is the differance between normal bybass & maintenance bybass in UPS?

1 Answers  


MCB is used for high rating &MCB is used for lower rating.What is technical difference between ACB & MCB?

7 Answers  


3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.

0 Answers  


What is Primary And Secondary Injection Test of Relay and Other Electrical Devices. How IT is carried out.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)