when a primary current injection test is required, it is
accomplished by what?
Answers were Sorted based on User's Feedback
Answer / mohammad farman khan-abu dhabi
Primary current injection test require at time of
commissioning to distrubution switchgear.High pot theory.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / brijesh
Primary current injection test require at the time of
commissioning to the current transformer.
The purpose of it is to check the ratio of C.T.
and for checking of C.T. circuit.
The test is conduct by means of primary injection test set.
In test set there is a current transformer and variac.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / arvind negi
Primary current injection test require at circuit
protection equipment throw.
Is This Answer Correct ? | 0 Yes | 2 No |
how we can measure the dc current instead of clamp meter ?
why transformer is rated in kva instead of kw?
how can we calculate air compressure capacity
What is electrical charger?
Why does the power consumed is always constant even if a fan speed is altered?
what is the min and max ohmic resistance for the earthing rod installed for lighting poles for street light network
how does commutator convert a.c to d.c?
0 Answers NRSC National Remote Sensing Centre, RBC,
what is the difference between servo voltage stabilizer and general voltage stabilizer?
what is the differance between normal bybass & maintenance bybass in UPS?
MCB is used for high rating &MCB is used for lower rating.What is technical difference between ACB & MCB?
3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.
What is Primary And Secondary Injection Test of Relay and Other Electrical Devices. How IT is carried out.