HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM
Answers were Sorted based on User's Feedback
Answer / kalirajan.n
TAKE A LOOK IN THE FORMULA BELOW....
VD= 2*K*I*L/ CSA
WHERE:
VD= VOLTAGE DROP
I= CURRENT
L= DISTANCE OF THE LOAD FROM THE OUTLET (IN FT)
K= 12 FOR COPPER AND 19 ALUMINUM (FOR MAXIMUM TEMP OF 75 DC)
CSA= CONDUCTOR CROSS SECTIONAL AREA IN CIRCULAR MILS.
Is This Answer Correct ? | 55 Yes | 20 No |
Answer / himadri nayak
Copper Wire
Single Phase/Circuit
Voltage 240
Power(W) 1000
Power Factor 0.8
Resistivity(at 15 c) 1.72E-08
Tempertature 35 C
Resistivity 3.096E-08(for copper)
Length(m) 300(phase+neutral)
Cross section(m2) 0.000006
Resistance 1.55
Load 5.21
Voltage drop 8.06
Percentage 3.36(Do not go above 3 %)
Actual voltage 236.64
Actual Current 5.28
This is a sample of how to calculate wire size for single phase copper wire. If you want contact me for the excel sheet for copper/Al, 3phase/1 phase calculation.
@ himadrinayak@yahoo.co.in
Is This Answer Correct ? | 31 Yes | 5 No |
Answer / dilawar husain
yes,these factors are important for cable sizes.
Is This Answer Correct ? | 25 Yes | 7 No |
Answer / venkat iyer
Factors that to be considered are;
1. ambient temperature
2. permitted temperature rise
3. factors applicable due to method of cable laying
4. factors applicable for group running of cables
5. spacing between cables
6. permitted voltage drop say 2.5%
Is This Answer Correct ? | 24 Yes | 7 No |
Answer / jignesh panwala
IT IS BAISICALLY DPEND UPON THE LOAD.
SUPPOSE 53 A LOAD.
53/1.5= 35 HP
35*0.746=26 KW
26000/690=38 SqMM
THIS CALCULATION IS FOR AL CABLE
Is This Answer Correct ? | 34 Yes | 20 No |
Answer / sivakumar
As per answer no 5, how you take 1.5 and 690 values for
calculation? is there any reference about that value
Is This Answer Correct ? | 22 Yes | 8 No |
Answer / rajnikant
Dear himadri,
i need more details for the calculation of copper and
aluminium sizes of cable and current capacity.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / bubbly
Actually all brothers we want to know calculation of cable
not VD so please any one have calculation of cable on load
& distance attach here
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / kalirajan.n
***SUPPOSE WE USE COPPER CONDUCTOR AND WE ALLOW A MAXIMUM OF
5V MAX. VOLTAGE DROP:
5= 2*12*15*230/CSA
CSA= 82800/5
CSA= 16560 CM
FROM COMMERCIAL REFERRENCES:
15560 CM IS CLOSEST TO 16510 CM WHICH IS #8 COPPER OR 8 SQMM
WIRE.
NOTE:
1. IN THIS CASE A MAXIMUM OF 5 VOLTS WAS CONSIDERED IN THE
CALCULATION.
2. THIS CALCULATION IS NOT VALID FOR LARGE MOTORS. BECAUSE
MOTORS DRAWS A MAXIMUM OF 7OO% TIMES ITS FULL LOAD TORQUE
DEPENDING ON THE MOTOR CONTROL STARTING METHODS USED BY THE
DESIGNING ENGINEER.
Is This Answer Correct ? | 14 Yes | 8 No |
Answer / rohit
Dear himadri nayak could you please tell me the formula to
calculate V.D...and exact formula for calculation of cable
size..but not taking any factor as assuming,,,and if u r
assuming then hw ur assuming????dear you can mail it to me
if you dont mind..
Thanks & regards
ROHIT
waiting for your reply ASAP....
Is This Answer Correct ? | 5 Yes | 2 No |
what is the function of choke in tube
How the neutral earthing is connected in DG alternator
Why Transformer does not work in DC ?
how we calculate torque ? how we improve it ?where torque will either motor or generator ?
WHAT IS MEAN BY MAGNETIC LOCKING
why not starting switch first connect in direct on line starter?????
what is reactive power?
where this neutral connection goes after returning from the load(home ,factory,industries).Is it grounded at the transformer side or atthe generator side .If it is grounded then we also ground the earth connection.is there any problem with this.
How many current ratings of MCB's are in the market? e.g: 1A, 2A, .......upto.
WHAT IS THE DIFFERENCE BETWEEN SHOP DRAWINGS/ DESIGN DRAWINGS AND AS BUILT DRAWINGS??
2 Answers ACC, Al-Jaber, Dubai Group, ECEC,
What is the frequency of dc current????
what is the difference between UPS and INVERTER?