What is the formula for finding fault level of generator?
Answers were Sorted based on User's Feedback
Answer / ramesh
I would like to answer by way of an example:
Generator capacity = 12MVA
Generator sub-transient impedance = 12%
With above two data,
the generator fault level can be calculated as folows:
Generator fault level = Generator capacity / generator sub-
transient impedance
Generator fault level = 12 MVA / 12% = 12MVA/.12 = 100MVA
To get fault current = Generator fault MVA / (1.732 *
generator rated voltage)
In case of single phase generator 1.732 to be ignored.
Is This Answer Correct ? | 49 Yes | 4 No |
Answer / ramesh
From your question I guess there is transformer between the
11kV & 6.6kV you are refering to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / dhiren patel
what is the refected current in 6.6 KV system in case of 11
kv side fault current is 40 KA and 8000 A full load current.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / mnaoj sharma
Ramesh whats ur Email ID .I want to know more about you. I
mam electrical engineer . Your answers are absolutely right.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / jignesh
we have 3 sets of generator running in parallel gen data 11kv 2000kva 1600kw transient reactance 0.1772and sub transient 0.1998 NGR 63.2 ohm . What is the fault level and fault current ? Please give me the solution on my mail id
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
RAMESH WTS UR EMAIL ID.....SEND ME UR EMAIL ID AT MY ID ...MY ID IS vinodmemoria07@gmail.com
i need ur help plz 4ward
Is This Answer Correct ? | 0 Yes | 1 No |
From your question I guess there is transformer between the
11kV & 6.6kV you are referring to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
mail-behera.ramesh@orisysinfotech.com
Is This Answer Correct ? | 0 Yes | 1 No |
explain Xmer
what is the minimum recommended leakage current of an earthed cable connected to the body or skid of an alternator
what is the reason the main breaker is trip during the motor is running? (some time the breaker is not trip)
What is the difference between switch gear and control gear ?
How Flywheel run in DG set, tell in details
why we commonly use delta star winding in power and distribution transformers
WHAT HAPPEN WHEN CT SECONDARY OPEN DURING LOAD
whatis the test procedure for lightning arrester which was installed one year back. i want check it whether it is working or not.
limitation of conductor height on ground when we consider EMC
What is spill current in protection relays?
What is the Load Capacity of Panther conductor (0.2) and dog conductor (0.1)
What is the Gap Should maintain for HT cables crossing of LT Cable?