how can calibrate vacume trasmitter by HART COMMUNICATOR ?
Answers were Sorted based on User's Feedback
for ex: the range is -760 to 0mmhg .
by following procedure we can calibrate the transmitter by
using hart
1.give the supply to transmitter
2: connect hart to transmitter with 250ohms series resistor
3.switch on the supply
4. hart shows device connected
5. go to process parameter and change the follwing
parameters
LRV:760mmhg
URV:0mmhg
then press send .then cross check the transmitter with
master pressure calibrator
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / senthilkumar
for ex: the range is -760 to 0mmhg .
by following procedure we can calibrate the transmitter by
using hart
1.give the supply to transmitter
2: connect hart to transmitter with 250ohms series resistor
3.switch on the supply
4. hart shows device connected
5. LRV= (-)760 mmHG URV= 0 mmHG
6. apply pressure 760 mmHG to low pressure side and see the
output it will show 20mA.
Is This Answer Correct ? | 2 Yes | 5 No |
How to calibrate Toxic gas detector?
How to change dcs card in online. (Dsc is maxdna)
can anyone guide me how to get any of the previous year GAIL question papers? are they available? 0n 2nd august i have to take the written test.
What is eddy current? Describe the operating principle of proximity probe.
What will the new flow factor if D/P Transmitter is RE-RANGED from 25" WC to 50" WC
Explain the difference between mmwc and mmwg?
what is the calibration standard for pressure and differential pressure transmitters?
Boiler flame scanner working principle?
How can we test a bently nevda 3500/42M accelerometer monitor card by simulating it with test equipment?. what king od of signal (milli volts or volts or or resistance ) we should feed in the terminals of the card?
Why we use 4 - 20 ma?
you must show the examples application and give at least 4 types of transducer/sensors that can minimize the failure during the manufacturing of the resistors.
What is the IEC Standard for PLC I/O Terminal wiring Procedure?