For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?
Answers were Sorted based on User's Feedback
Answer / mugil
below 250 mtr you can use 1.5 sqmm and above 250 you should use 2.5 sqmm.Because if length is increasing voltage drop will increase that is the reason we are increasing cable the core size.
Is This Answer Correct ? | 10 Yes | 2 No |