How to calculate busbar size & what is the procedure we
make for determine that?
Answers were Sorted based on User's Feedback
Answer / sujata wagh
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
Is This Answer Correct ? | 246 Yes | 46 No |
Answer / ashraf majid
The busbar size will be determined by the total loads
connected to the bus.This will require a comprehensive
study of nature of loads plus the surroundings of place.
The general procedure will be such that the operating
parameters don't voilate the maximum safety limits of the
bus.
Is This Answer Correct ? | 145 Yes | 65 No |
Answer / kajajohn
to calculate bus bar size normally for copper 1 sqmm =1.3 A
for aluminium 1 sqmm =0.8 Amps
Is This Answer Correct ? | 129 Yes | 49 No |
Answer / bhavin shah
busbar sizes can not be calculated only from overall size.
there are various derating factors like arrangment of
busbar, nos of busbar, spacing, enclouser size, ventilation
in room, temp rise, skin effect, proximity effect etc.
which need to be consider while designing the busbar.
Is This Answer Correct ? | 64 Yes | 15 No |
Answer / akmal
i want to add in vijay answer that the qulity of copper also
depend on amper rating of coper bar
Is This Answer Correct ? | 65 Yes | 22 No |
Answer / jaydev jena
current density= .8 amp/sqmm.that does mean 1sqmm can carry
0.8 amp current .if sisze of busbar is 100mmx 10 mm then it
can carry 800 amp.
Is This Answer Correct ? | 61 Yes | 25 No |
Answer / nikhan
The bus bar size normally for copper 1sqmm=1.3Am and
aluminium is 1sqmm=0.8Amp
Is This Answer Correct ? | 53 Yes | 20 No |
Answer / waves
Generally current carrying capacity of Al. is 0.8A per
sqmm and Copper is 1.6A per Sqmm.
Suppose we need bus bar for 630A, and we are going with
Aluminium bus bar
= 80*10*.8=640A
where 80*10 is size if bus bar usually available is the
market.
so we can use 80x10sqmm al. busbar per phase for 630A.
for TPN- (3.5)x80x10
If we are going with Copper bus bar
than we will use = 40x10sqmm per phase
= 40x10x1.6=640A
where 40*10 is size if bus bar usually available is the
market.
so we can use 40x10sqmm copper busbar per phase for 630A.
for TPN- (3.5)x40x10
Is This Answer Correct ? | 40 Yes | 7 No |
can you give any example at any parameters?
Is This Answer Correct ? | 62 Yes | 37 No |
Answer / md.mahmudul hasan
we need to consider short ckt(KA) also. Say short ckt level
is 20KA then we need to select busbar accordingly.
Is This Answer Correct ? | 30 Yes | 5 No |
good morning sir, can u please tell me what type of questions asked in jindal so i can do my best in exam.
What are the components connected in between the power supply coming from an electric pole to HT & LT Panels in a large commercial building or how the power supply connected from Electric pole to Transformer & then to the HT & LT panels of a building? Please send me answers via mail, my id is yogiagarwal@gmail.com. If possible, please give a line diagram.
how to get electrical supervisour certificate in gujarat
. What should be the minimum and maximum ohmic value for earthing?
our company have 750 kva oil transformer.still we have facing a problem that is when voltage is 11.5 kv coming from HT side then LT-side voltage is 420v or above at tape 1.please give me best solution to decrease the voltage.
how can we represne the analog signal and digital signal if want to measure the speed and we have to use PLC
How are harmonics produced in AC machines?
how does an centrifugal and screw type chiller will work. which chiller efficiency is high and why.
state working of halogen lamp?
WHY WE NEED NEUTRAL FOR 3PH 400 OR 415 VOLTS POWER SUPPLY (4 WIRE SOURCE).
Why pmg used in electrical generators for excitation.is there any other method without pmg ?
1) Why distributiion system decided 11 kv, 33 kv, 66 kv, 132 kv, 220 kv, 400 kv, 2) In 3 Phase line terminal of capacitor, why used for power factor improvement. 3) Why used rating KVA in transformer?