11kv/0.433kv, 2 mva , transformer , for protection and
metering how many CT/PT are required?
Answers were Sorted based on User's Feedback
3 line PT's prot./meter in 11kv side(before side)
3 prot/meter. CT's at 11kv side(before side)
3 line PT's prot./meter in .433kv side(after side)
3 prot/meter. CT's at .433kv side(afterside)
In each CTs & PTs,ther wil b a seperate core for metering n
protection,dont get confused with the windings in assuming
tat this is for ef,oc and differential,get a CT/PT wit both
metering n protection whatevr d core is depends upon our
application in relays.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manax
transformer primary side one set (3 nos) ct,pt and
secondary side one set ct,pt required.each ct pt consist 2
core one for metering,one for protection.this LT
Transformer so no need any special protection.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.k.mishra
3 ct having 3 core for metering & protection
3 pt for mounted R,Y,B induvisualy for metering & protection
also 1 neotral ct is requried for star connection
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jesudoss
transformer secondary (433v)-3 ct for over current
-1 ct for restrictedearthfault.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vishal
3 CT's and 3 PT's wil; be required for each phase of transformer
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / d.k.sahu
At primary side 3 nos ct for metering & protection,1 no
cbct & 3nos pt.
At secondary side 3nos ct & 3nos pt.
Total ct/pt : 13no
Is This Answer Correct ? | 0 Yes | 0 No |
Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise carrying amps rating.Please give the solution with a good example.
why square root 2 is multiplied with line voltage in selection of LA ie 11/sqrtroot3=6.35 kv and it is multiplied with sqrt2 ie 6.35 KV*sqrt2=8.9 kv we will select 9kv.my question is why we are multiplying with sqrt 2?
The size and construction of bushings in a transformer depend upon?
1 HP = how many Kva
What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?
Reason of secondary of ct always short
which type of winding is used for high voltage & low current?
wich types of current?
what are the different sizes of U.G. cable & where these cabl;es are used according to voltage ..
why motor run slow speed in star connection?explain how?
In simply words(not explain any formula )what do you mean by power factor.?
i have 6oo kva dry type transformer and its neutral is not grounded even body of transformer ground i want to know it is safe or not ?