I have 30 kw motor load & i have selected 10 kvar capacitor bank for power factor improvement.my existing p.f is 0.85 & proposed p.f is 0.99 so ,is it right selection?
2 nd question how to connect c.bank whether in delta or star connection & how to decide it?
as per electrical calculations if we want maintained .99 pf we should have 14.31KVAR is sufficient.
| Is This Answer Correct ? | 2 Yes | 0 No |
why transformer impedance measure in % (percentage)
what is megar healthy value for ht < cables
Why Neutral Busbar CT & transformer neutral CT connected with phase CT in Restricted Earth Fault?
Explain the laying procedure and laying depth of submarine/subsea power cable for 220/400KV system? Also available cable diameter?
A 40 kva transformer has a core loss of 400W and a full load copper loss of 800W. What is The proportion of full load at maxmimum efficiency?
How to calulate Locked rotor amper(LRA) for compressor type motors?
how to can we synchronize different capacity of DG sets.60kva& 250kva?
Give some differences between open loop and closed loop?
11 kv line me tino phase takra jaye to present time me approximately voltage aur current kya hoga...
2 Answers Electrical, Electrical Tech, Videocon,
how to calculate
What the methode get earth resistance?
How we can change the direction of rotation of Induction motor? Prove it using graphical methods.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)