how to can we synchronize different capacity of DG
sets.60kva& 250kva?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Synchronization is as usual.The load sharing depends upon
fuel feed to prime movers
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / kj
As per the previous answer, synchronising is not a problem.
Using a load sharing module which is set up correctly will
allow the sets to share the load on a percentage basis. In
other words if the load is say 200 kva the load would be
about 65% on each or 38 kva and 161 kva.
Is This Answer Correct ? | 2 Yes | 0 No |
What is magneto on a gas generator. how it functions. its out put is d.c or a.c. how it can be checked for correct functioning
How the real power output is controlled in a Generator?
operation principle of a generator? Gss, Diesel and HFO which is better and why?
How can get electrical c licence.Now i am working in spining Mill , transformer capacity 2750kva. Sanction demand 2250kva. Please advise me . My contact no 09944226823
5 Answers Pace Power Systems, VRVS, VSJ Industry,
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
what are the points to be consider for MCB(miniature circuit breaker selection?
what is a panel board?
10 hp motor ,7.5 kw ,960 rpm, full load current 15.5, delta connection so how much take current no load trial time. any formula please give..... second question :- what is different between brekar control wiring and motor starter control wiring
What is difference between Ac Voltmeter And Dc Voltmeter ????
What is the difference between Dielectric and Insulator
how much Amp we can put in 1200kva generator?
how to convert psi into kilo pascal? what is the suction pressure & discharge pressure of chiller?