Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why Neutral Busbar CT & transformer neutral CT connected
with phase CT in Restricted Earth Fault?

Answers were Sorted based on User's Feedback



Why Neutral Busbar CT & transformer neutral CT connected with phase CT in Restricted Earth Fau..

Answer / vinod g

In Restricted earth fault protection Three phase CT is
parralleling (shorting all S1 andshorting all S2 together)
and paralleel conection with Neutral Relay and CT. IN
Healthy conditon current in all the three phase will be
balanced and summation will be zero. During earth fault out
side CT area summation of phase CT currents and Neutral CT
zero, so relay will not pick up. When earth fault inside
the transformer the current in the CT will differ and Relay
will pick and trip the tranformer breaker,so it is clear
that REF is for Transformer Winding protection and Bushing
CT is normally using for phase CT

Is This Answer Correct ?    3 Yes 0 No

Why Neutral Busbar CT & transformer neutral CT connected with phase CT in Restricted Earth Fau..

Answer / pintu

THIS IS CALLED 5 CT CONFIGURATION (3 PH. CT + 1 X'MER NCT +
1 BB N CT)OF REF PROTECTION. ALL THESE FIVE CTS ARE TO BE
CONNECTED IN PARALLEL. TRANSFORMER NCT SHOULD BE LOCATED
AFTER NEUTRAL BIFERCATION (I.E. PATH TOWARDS EARTH) AS THIS
IS DEDICTAED FOR DETECTING THE RESIDUAL CURRENT IN CASE OF
GROUND FAULT. BUT NEUTRAL BUSBAR CT IS NOT FOR DETECTING
THE FAULT CUURENT BUT FOR THE UNBALANCE CURRENT IN THE
SYSTEM. IT SHOULD NOT BE TRIPPED DURING THE EARTH FAULT.

IN 4 CTS CONFIGURATION OF REF PROTECTION, NEUTRAL BUSBAR CT
CONNECTION WILL NOT BE THERE. YOU SHOULD DECIDE THE 5 OR 4
CT CONFIGURATION AS PER YOUR SYSTEM DESIGN.

Is This Answer Correct ?    3 Yes 2 No

Why Neutral Busbar CT & transformer neutral CT connected with phase CT in Restricted Earth Fau..

Answer / anup mahajan

The purpoae of Restricted earth fault (REF) is to provide
the protection of transformer neutral in case of residual
current. As the fault which lies near phases are known as
external faults and is to be detected by differential
protection but the residual current which is not going to
ground and circulates between neutral and phases are
detedted by REF protection. Please keep in mind that CT
characteristics of this REF must be matched with phase side
CT characteristics.

Is This Answer Correct ?    2 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

What if high voltage side circuit breaker of a ehv transformer instead of lvcb? Kindly elaborate.

0 Answers   MSETCL Maharashtra State Electricity Transmission Co Ltd,


What is RSS Meter

0 Answers   Krishna Constructions,


how can we determine size of a cable by knowing the kw or current rating of a load?how can we calculate the resistance box of a slip ring motor?

0 Answers   TK Group,


What is earth system using on the floater TN-S or TT. Iam not sure and what ICCP

0 Answers  


what is the difference between relay and a contactor.

5 Answers   Siemens,


I AM A ELECTRICAL PANEL BOARD DESIGN ENGINEER.IF I GO ANY INTERVIEW ,TECHNICALLY WHAT ARE QUESTIONS I WILL FACE FROM INTERVIEWER?

0 Answers   Bell,


briefly explain the main blocks found in a microprocessor based system

0 Answers  


What is inrush current? how can calculateit? what is the affect of it?

0 Answers  


what is the maximum load in MDB,SMDB and DB

1 Answers  


Difference between on line capacitor and Station type capacitor.

1 Answers  


Whta is earthing?What is the optimum value of Earth Pit?

2 Answers   Bharti,


hy i need help with LabView, I need a sample code of LabView to download serial data from the Intellivue Patient Monitor to PC. Thank you in advance.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)