why should a transformer be never connected to dc supply
Answers were Sorted based on User's Feedback
Answer / shantanu
the transformer action is not possible with dc of constant
magnitude as the flux will not be genrated btwn primary &
secondary winding ..
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / sivakumar
it mean we are applying dc(constant) current to coil ,voltage is zero across inductor(transformer winding) so there is a short circuit occuring so it draws high current
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abhinav kumar
Ac voltage waveform is alternate so genrate a mutual induction and dc is direct current so it is not genrate mutual induction
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bapan
If Dc supply is given to atransformer there will be no change in the flux with time.so,there is no emf induced in the primary and secondary winding and hence transformer action will not take place.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / r. p. siroih
The transformer works on the basis of to transfer the energy (votage) to stepping down or up in alernative mode. In the DC power the current flow in streight line, so transformer can not transfer the voltage .
| Is This Answer Correct ? | 0 Yes | 0 No |
difference between substation & grid substation?
Type of cable insulation?
why we use only sine wave in ac why we do not use other wave forms
how can i improve the power factor in domestic (230v)
hi friends i m from electrical branch and seeking for tech. + apti. both papers of hpcl plz get it available as soon as possible
0 Answers Engineers India, Engineers India Limited,
short notes on npn & pnp transisitor..........
What is the distance between each insulator in 33kv transformer and how can it calculate
IN induction motor pf is increased using capacitors.what will be the effect on motor and system when very large capacitor is accidently installed and pf goes leading.
A 400 V, 50 Hz, Δ connected synchronous generator has a field reactance of 0.1 Ω and armature resistance of 0.015 Ω. At full load, the machine supplies 1200 A at 0.8 pf lagging. Under full-load conditions, the friction and windage losses are 40 KW and the core losses are 30 KW. What is the machine’s overall efficiency? Ignore any field circuit losses.
why does a dc machine has high efficiency while working as a generator than as a motor
wat is the current produced in a 5000v megger? when the positive and negetive terminals are touched on our body get s shock?
why mostly conductor made by 7 nos wire?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)