in short circuit. test of a
transformer 5 to 10%
ofvrated voltage is used why??? if
we use rated
voltafe then what will be?
The 5-10% of rated voltage represents the short-circuit
voltage that means if you connect all the secondary
terminals of the transformer together-it is a “short-
circuit”. If you supply the primary winding terminals this
short-circuit voltage you’ll get the rated current-primary
and secondary.
If the supply voltage is the rated voltage you’ll get the
short-circuit current [10-20 times the rated].
Is This Answer Correct ? | 0 Yes | 0 No |
WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?
why ct is connected at bushing of transformer ??????????
What is spill current in protection relays?
PLC Training in chennai | PLC Training institute in chennai, PLC Training center in chennai | Best PLC Training in chennai | PLC Training course in chennai | SCADA Training in chennai | PLC Training in india
why generator one end side star neutral point given? if this point not given what happen?
why star point of HT motor not earthed?
what is the pperating squvance in transmission line for circuit braker, isolater & earthing switch.
Classify driling machines.
What is mean by % impedance of transformer? detail explanations expected.
Seamless tubes are made by?
What is FM200 Fire Supresion System??
How can we findout the maximum efficiancy of Transformer? At which load?