Resistance Grounding falls into two categories: Low
Resistance and High Resistance
1) In Low Resistance Grounded (LRG) Systems the current is
limited to 25 amps or more. Generally the range is from 25
to 600 amps, although in some systems it may be even
greater.
2) In High Resistance Grounded (HRG) Systems the current
is limited to 10 amps or less.
------------
A) On systems with a voltage of 1000 volts or less (phase-
to-phase) grounding resistors are not used. Normally these
system use a solidly grounded configuration with no
intentional impedance being introduced into the system.
B) Resistance Grounding is recommended on Medium Voltage
Systems from 1000 volts to 15,000 volts phase-tophase.
C) Because of the cost, Resistance Grounding is not usually
used on systems above 15,000 volts phase-to-phase.
Additionally, the use of a solidly grounded system allows
for use of equipment which is insulated for the
phase-to-neutral voltage of the system.
·D) When a system has protective relays which will trip the
circuit if a ground fault occurs, a grounding resistor with
a 10 Second Rating is often specified, because the relays
will trip the system in less than 10 seconds.However, One
Minute or Ten Minute ratings are sometimes used for an
extra margin of safety, even though the cost will be
greater.
| Is This Answer Correct ? | 5 Yes | 0 No |
Resistance Grounding falls into two categories: Low
Resistance and High Resistance
1) In Low Resistance Grounded (LRG) Systems the current is
limited to 25 amps or more. Generally the range is from 25
to 600 amps, although in some systems it may be even
greater.
2) In High Resistance Grounded (HRG) Systems the current
is limited to 10 amps or less.
A) On systems with a voltage of 1000 volts or less (phase-
to-phase) grounding resistors are not used. Normally these
system use a solidly grounded configuration with no
intentional impedance being introduced into the system.
B) Resistance Grounding is recommended on Medium Voltage
Systems from 1000 volts to 15,000 volts phase-to phase.
C) Because of the cost, Resistance Grounding is not usually
used on systems above 15,000 volts phase-to-phase.
Additionally, the use of a solidly grounded system allows
for use of equipment which is insulated for the phase-to-
neutral voltage of the system.
D) When a system has protective relays which will trip the
circuit if a ground fault occurs, a grounding resistor with
a 10 Second Rating is often specified, because the relays
will trip the system in less than 10 seconds. However, One
Minute or Ten Minute ratings are sometimes used for an
extra margin of safety, even though the cost will be
greater.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / john
HRG - High resistance grounded.
LRG - Low resistance grounded
| Is This Answer Correct ? | 2 Yes | 0 No |
WHAT IS B & C CLASS SURGE PROTECTION AND WHAT IS DIFFERENCE BETWEEN B & c CLASS SP
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
why mosquito bat makes noise when it hits with a insect?
how solar power plant energy meter multiplication factor
Why motor is not calculated in kva, whereas transormers are calculated in kva
Hysteresis loss in a core is due to what reason or property of the material used for that core?
Why we connect the capacitor in Delta?if we conect in Star what will happen?
Differentiate between power relay and reverse power relay?
what are the standard transmision voltages in india?
What is the meaning of 40X8X2 busbar dimensions for carring load of 400 Amps
we have 3*1 MW generator one NGR is common for all it will be selected during paralle our problem is two generator ca be paralled but when slecting third one we need to close NGR selection on third one other wise voltage not matching why?
If only R Phase is connected in 2 pole elcb, n is not connected than it will work or not in ground fault.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)