Resistance Grounding falls into two categories: Low
Resistance and High Resistance
1) In Low Resistance Grounded (LRG) Systems the current is
limited to 25 amps or more. Generally the range is from 25
to 600 amps, although in some systems it may be even
greater.
2) In High Resistance Grounded (HRG) Systems the current
is limited to 10 amps or less.
------------
A) On systems with a voltage of 1000 volts or less (phase-
to-phase) grounding resistors are not used. Normally these
system use a solidly grounded configuration with no
intentional impedance being introduced into the system.
B) Resistance Grounding is recommended on Medium Voltage
Systems from 1000 volts to 15,000 volts phase-tophase.
C) Because of the cost, Resistance Grounding is not usually
used on systems above 15,000 volts phase-to-phase.
Additionally, the use of a solidly grounded system allows
for use of equipment which is insulated for the
phase-to-neutral voltage of the system.
·D) When a system has protective relays which will trip the
circuit if a ground fault occurs, a grounding resistor with
a 10 Second Rating is often specified, because the relays
will trip the system in less than 10 seconds.However, One
Minute or Ten Minute ratings are sometimes used for an
extra margin of safety, even though the cost will be
greater.
Is This Answer Correct ? | 5 Yes | 0 No |
Resistance Grounding falls into two categories: Low
Resistance and High Resistance
1) In Low Resistance Grounded (LRG) Systems the current is
limited to 25 amps or more. Generally the range is from 25
to 600 amps, although in some systems it may be even
greater.
2) In High Resistance Grounded (HRG) Systems the current
is limited to 10 amps or less.
A) On systems with a voltage of 1000 volts or less (phase-
to-phase) grounding resistors are not used. Normally these
system use a solidly grounded configuration with no
intentional impedance being introduced into the system.
B) Resistance Grounding is recommended on Medium Voltage
Systems from 1000 volts to 15,000 volts phase-to phase.
C) Because of the cost, Resistance Grounding is not usually
used on systems above 15,000 volts phase-to-phase.
Additionally, the use of a solidly grounded system allows
for use of equipment which is insulated for the phase-to-
neutral voltage of the system.
D) When a system has protective relays which will trip the
circuit if a ground fault occurs, a grounding resistor with
a 10 Second Rating is often specified, because the relays
will trip the system in less than 10 seconds. However, One
Minute or Ten Minute ratings are sometimes used for an
extra margin of safety, even though the cost will be
greater.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / john
HRG - High resistance grounded.
LRG - Low resistance grounded
Is This Answer Correct ? | 2 Yes | 0 No |
what are the components in electrical control panel (for example: 415V, 3-ph, panel to operate utility and 3-ph DG set).
If more than rated DC voltage appears across trip coil of the breaker, what will happen? e.g. in 110V DC circuit system, if voltage across battery terminal showing 121 V
What is bridge rectifier and explain with details
i have three phase 25kva transformer but there is two phase line how can i connect to the two phase line?
What is application of MCB & How it works
is there any chance to get shock from the transformer oil at the time of maintenance due to its dielectric property. . ?
what is synchronizing panel & its working.
what is tertiary winding in transformer?What is its purpose?
our company have 750 kva oil transformer.still we have facing a problem that is when voltage is 11.5 kv coming from HT side then LT-side voltage is 420v or above at tape 1.please give me best solution to decrease the voltage
why voltages are added when batteries are connected in series?
1)why the transformer rating in KVA insted of KW 2)why the secondary of ct is shorted and why the PT secondary is open
1 HT service how many LT Service