why farmers are use earthing instead of neutral for their light conec. at
field.is it safe
Answers were Sorted based on User's Feedback
As there is a vast difference between the Earth & Neutral
The ground or "earth" wire is a circuit's safety protective
wire that normally carries no current.
It is there to force a fuse to blow or a circuit breaker or
GFCI to trip if a fault condition occurs in any appliances,
their flexible cords or plugs that are connected into the
circuit.
By carrying away the excess current in a fault condition -
which should cause the protecting fuse to blow or circuit
breaker to trip - the "ground" or "earth" wire protects the
building and its occupants because the power should be cut
off before anyone gets electrocuted or any overloaded
circuit wiring or appliances catch on fire.
The neutral is the normal "return" wire: in systems where
the load is supplied from only one hot (or "live") wire, the
neutral completes the circuit and carries current back from
the load to the power station.
All the neutral and ground (or "earth") wires in a building
are tied or linked together at the incoming service main
breaker panel. This is the only place they should ever be
tied together because it is "upstream" of all the fuses
and/or circuit breakers protecting the hot (or "live") wires
for the various circuits installed in the building.
Warning: we must never assume that a neutral is safe to
touch: it has to be checked with a voltmeter or a voltage
indicator to be sure it is not "live". This is because a
neutral wire is designed to carry current under normal
circumstances.
So, if a neutral wire going back to the incoming main
breaker panel has not been properly connected - or suffers a
deliberate disconnection or some accidental damage which
causes it to break - then it and any neutral wires connected
to it further downstream will go live up to the break
because of being connected to the downstream loads which
still have hot feeds coming into them!
That is why we should never use a neutral as a substitute
for a proper, separate, ground or "earth" wire.
| Is This Answer Correct ? | 2 Yes | 1 No |
what is the size of ht cable of 33kv ht line and transformers ratings are 2.5mva and 5.5mva.please send formula also.
How to calculate Battery back up time for a 400 AH Battery bank having a load of 20 Amps and charging time required to fully charge this battery bank?
i purchase a microwave which is 50/60Hz but Current Setting 60Hz in my country we usually use 50hz, can i use AVR to solve my problem?
What is the usega of brking resistor? and how it will useful to Drive...?
Why we did not feel electric shock in electric train?
what is the speed of mixie?
why root three is used and how its comes in three phase power system?
why induction motors are rated at 0.8 power factor.
what happen to a dc series motor if it given as ac supply accidentaly
in railways why we use the power in 10,20 30kv,why not in the multiple of 11kv
what happens if the phase sequence of parrlel connected sys will changed & phase displacement
what is vA rating and class of a ct.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)