we want install 11KV generator to supply power 12km far
from the power house.Load to be fed is 1MW.which conductor
should we use and wat will be transmission line losses?
Answer / k.prakashchandra
The current is 52.5 A at unity pf, add 20 % .It is about 60
A. You can use Rabbit conductor
Is This Answer Correct ? | 0 Yes | 1 No |