how many testing use in power transformer?tell equipment
names?
Answers were Sorted based on User's Feedback
Answer / pradeep
There are so many testing are available to test a power transformer.
1. Turns ration testing : to ensure the no.of turns on each winding.
2. Winding resistance testing: To measure the resistance of each winding.
3. Vector group testing : To identify transformer vector group, which is very important for parallel operation.
4. Insulation resistance testing : To ensure the healthiness of transformer insulation resistance.
5. Impedance voltage testing : Important for parallel operation and loading condition assessment.
6. No load/ Short circuit testing : For the measurement of losses.
7. Partial discharge testing : To monitor the insulation imperfection/aging effect
8. Switching impulse/ lightning impulse testing : To measure the impulse withstand strength of the transformers.
9. Acoustic level measurement: To track the level of magnetic hum of the transformer.
10. Dissolved gas analysis: To identify dissolved gaseous in the transformer gases.
11. Dielectric testing : To measure break down potential of transformer oil.
And the count goes on...!!!
The type of testings carried out will vary based on the application and criticality
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sudhakar g
HI,
Power transformer is used in Switchyards where it can
supply the voltage from grid to grid and the strutcure of
the transformer is Delta to Delta connection. there is no
stepup or step down in that.
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 1 Yes | 2 No |
IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP TO 280 SO CAN I USE ONE LOWER KVA DG SET WITH STEP UP TRANSFORMERS THAT MEANS WITH LOW POWER INPUT TO GET CONSTANT HIGH POWER OUTPUT EG:125KVA DG SET = 250 KVA STEP UP TRANSFORMERS
Totally how much power will be consumed in 1 hour cotinuous running of electric train engine?
How to select AC3 duty contactor for DOL & Star-Delta starters
how MW increase when steam input increase in turbine.
what types of electrical & mechanical test conducted in switchyard?
Welding machine
how to stop oil leakage in power transformer.
How i can calculate the cable size for given load,there is any formula,for 3 phase and single phase
2 Answers Prescient Technologies,
how we can improve P.F. by using capacitors ?
what is distribution board?
What are the condition for parallel operation of transformers?
What is meant by pilot exciter and its working?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)