IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP
TO 280
SO CAN I USE ONE LOWER KVA DG SET WITH STEP UP TRANSFORMERS
THAT MEANS WITH LOW POWER INPUT TO GET CONSTANT HIGH POWER
OUTPUT
EG:125KVA DG SET = 250 KVA STEP UP TRANSFORMERS
Answer / sudhakar g
Generally if u take125HP if we converted in to KW it will come 93.75KW only we can use...
I=(93.75*1000)/(1.732*415v*0.8)
I=163A
this is the maximum current we can use at full Load then how you are using upto 280A....
I think it is not possible...Correct me if i am wrong...
In your second case it is not possible To genrate 125KVA DG set to 250KVA Stepup transformers bcoz if we saw in Generation or transmission of supply the 400KV or 200KV lines there we can use 3 MVA transformers for stepup or Stepdown bcoz the input sully is capable to genrate the supply higher or lower......
According to IS standards the distance between pits must be
2.5mtrs and from the building it should be far from 3000mm
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
Is This Answer Correct ? | 2 Yes | 0 No |
Can anyone tell me what will happen if AC & DC supply get mixed???
What is the d/f b/w MCCB & MCB
Is there any Institution for giving M-tech in Electrical engineering for those who r in service? Give the details please.
How RTCC works with OLTC
Is it recommended to apply H.pot test for new cables segments after terminations or joints, however, this cable has been tested before at the manufactor by the vendor ? or only we can apply megger tests ?
What does the term power factor shows?
define electrical field?
What is I to C?
3ph line voltage 220v, how can run a 220v single ph motor or Light?
Give the two basic speed control of DC shunt motor.
which types of tests are required after commissioning of 6.6 kva tranformer?
why ht motors are connected in star?