How i can calculate the cable size for given load,there is any formula,for 3 phase and single phase
Answers were Sorted based on User's Feedback
Answer / jafar
for calculating cable size first we have to calculate load current
example 1 : 3KW POWER (1phase)
current i= 3*1000 /(230*0.8)
= 16.3A
for current carrying capacity of 1 sq mm copper is 2.4A
for current carrying capacity of 1 sq mm AL is 1.4A
now here if we use Cu then cable size is 16.3/2.4
= 6.79 is our calculated value
so we can choose near size of cable which is 10 sq mm
example 2 : 100W power (3 phase)
current i= 100*1000/(1.732*400*0.8)
= 180A
like that above
cable size is 180/2.4 = 75
so near size is 95 mm2
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / love kumar
for three phase copper cable is consider as 1sq mm ,3amp.
for aluminium cable 1sqmm -1amp
Is This Answer Correct ? | 0 Yes | 0 No |
hi, i have 3x200KVA and 2 x 80KVA UPS with battery bank of 150AH 68Nos. and 100AH 204Nos., i need to install AC either ductable or PAC type, so can you help me to calculate heat load and capacity of the AC to install.
Why PT voltages are measured with respect to ground? What do u mean by voltage or current polarized.
Why is better to have a minimum ceiling voltage of 250% than 160%?
what is deffrent alternatid and gernater
what are the main faults that occur in stabilizers? How they corrected and resolved ? Types of stabilizers ?
Why use the vcb at high transmission system ? Why can’t use acb?
how do using transformer 30 deg lag or 30 deg lead
why are using bus ducts ? why not using cables
IF we have three 30KW motor, these motors are connected in DOL, star-delta and VFD respectively, what will be the fuse rating for the above three?
what is the load amp for 1 HP 3 phase Motor ?
when a three phase motor in running condition consumes 2A in each phase,and if one of the phase gets fails what will be the consumption in other two phases
How to calculate capacitor bank size at a load 800kVA.