1. Insulation Resistance Measurement
a . For LT systems, use only 500V or 1000V Megger
b. For MV & HV systems, use 2500V or 5000V Megger
c. Remove Earth from Transformer neutral
2. Winding Resistance Measurement
R-N AND r-n
Y-N y-n
B-N b-n
3. Magnetic Current Test
Applied Voltage : RY YB BR
Measured Current : R Y B
4. Magnetic Balance Test
5. Vector Group Confirmation.
6 . Short Circuit Test and Differential Stability.
7 . REF Stability Test
8. Cooler Circuits.
9. Auxilliary Protection Circuits

Is This Answer Correct ?    2 Yes 0 No

In Transformer testing at Shop test we normally test for vector group, open ckt.,short ckt. but wha..

Answer / brahma

Also Double voltage double frequency, if customer ask impulse

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Transfer function is == ? a. Mathematical model b. System with no physical structure c. Can be calculated through differential equations

1 Answers   CCP,


how does excitation of brushless alternator took place?

1 Answers  


what is the purpose of fuse?

7 Answers  


Show the schematic arrangement of diesel power station layout and give its principle of operation.

0 Answers  


why dc series motor has high starting torque

2 Answers  






What is the size of a 60 watt and 80 watt tubelight?

0 Answers  


what is lrs tank water resistance.

1 Answers  


why does rotor rotets?

0 Answers   IBM,


How to convert resistance value at 20 degree to 90 degree?

2 Answers  


What is critical disruptive voltage?

0 Answers  


In radial network the source is fed from 1 end both ends at central

0 Answers  


The knee point of a current transformer is normally unique and known.So why in the nameplate of a CT they put the minimum value like this Vk> 400v.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)