In Transformer testing at Shop test we normally test for
vector group, open ckt.,short ckt. but what are the other
test performed for transformer once it reaches at site.For
e.g:if the transformer is dry having rating 1000KVA?
Answers were Sorted based on User's Feedback
Answer / guest
1. Insulation Resistance Measurement
a . For LT systems, use only 500V or 1000V Megger
b. For MV & HV systems, use 2500V or 5000V Megger
c. Remove Earth from Transformer neutral
2. Winding Resistance Measurement
R-N AND r-n
Y-N y-n
B-N b-n
3. Magnetic Current Test
Applied Voltage : RY YB BR
Measured Current : R Y B
4. Magnetic Balance Test
5. Vector Group Confirmation.
6 . Short Circuit Test and Differential Stability.
7 . REF Stability Test
8. Cooler Circuits.
9. Auxilliary Protection Circuits
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / brahma
Also Double voltage double frequency, if customer ask impulse
Is This Answer Correct ? | 0 Yes | 0 No |
Transfer function is == ? a. Mathematical model b. System with no physical structure c. Can be calculated through differential equations
how does excitation of brushless alternator took place?
what is the purpose of fuse?
Show the schematic arrangement of diesel power station layout and give its principle of operation.
why dc series motor has high starting torque
What is the size of a 60 watt and 80 watt tubelight?
what is lrs tank water resistance.
why does rotor rotets?
How to convert resistance value at 20 degree to 90 degree?
What is critical disruptive voltage?
In radial network the source is fed from 1 end both ends at central
The knee point of a current transformer is normally unique and known.So why in the nameplate of a CT they put the minimum value like this Vk> 400v.