Answer / ravi
Winding connection designations
High Voltage Always capital letters
Delta - D
Star - S
Interconnected star - Z
Neutral brought out - N
Low voltage Always small letters
Delta - d
Star - s
Interconnected star - z
Neutral brought out - n
Phase displacement
Phase rotation is always anti-clockwise. (international
adopted convention)
Use the hour indicator as the indicating phase displacement
angle. Because there are 12 hours on a clock, and a circle
consists out of 360°, each hour represents 30°.
Thus 1 = 30°, 2 = 60°, 3 = 90°, 6 = 180° and 12 = 0° or
360°.
The minute hand is set on 12 o'clock and replaces the line
to neutral voltage (sometimes imaginary) of the HV winding.
This position is always the reference point.
Because rotation is anti-clockwise, 1 = 30° lagging (LV
lags HV with 30°)and 11 = 330° lagging or 30° leading (LV
leads HV with 30°)
To summarise:
Dd0
Delta connected HV winding, delta connected LV winding, no
phase shift between HV and LV.
Dyn11
Delta connected HV winding, star connected LV winding with
neutral brought out, LV is leading HV with 30°
YNd5
Star connected HV winding with neutral brought out, delta
connected LV winding, LV lags HV with 150°
" So there is no specification of Dy11.. it will be Dyn11 "
| Is This Answer Correct ? | 63 Yes | 18 No |
Answer / pb
Dyn11 means Primary---Delta, Secondary---Star with neutral
brought out and secondary leading the primary by 30 deg
In case of Dy11 --- neutral is not brought out, rest
remaining the same as above.
| Is This Answer Correct ? | 28 Yes | 6 No |
Answer / sunny
thanks ravi
i had searched all over the net but didn't cleared myself.....
very easy & understanding
| Is This Answer Correct ? | 13 Yes | 7 No |
Answer / jim kirk
Mr Ravi
An excellent explanation - but there are DY11 transformers - we have two of them onsite
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kandavel .p
Thanks Mr Ravi i understood clearly ,your way of explanation is good thanks lot
| Is This Answer Correct ? | 2 Yes | 3 No |
What are the basic & Majour problems in UPS ?
0 Answers Roto Power, RotoPower,
why we need of power factor correction? give advantages
What is DC power factor??
how can we know the size of cable cross-section from current rating ?
if we apply 1000ADC instead of 100ADC or We apply 50ADC instead of 100ADC,What will be happened in the test result value.Pl explain
what will be d.g. capacity to cater together for 14hp A.C. load & 3kw lighting load
what is the purpose of the armored for the power Or control cable? How to select the type of the armored?
please let me know , we have installed two separate motor for fire fighting system 1) 60 hp and 2) 15 hp the load is 74 AMPS and 20 AMPS then tell me the main power cable in Aluminum will be what thickness , the length is 225 mt from the main utility to fire pump house
How can I model an open-delta ground transformer for a network supplied by 4 unit GTG and power transformer in ETAP?
if voltage bt phase & nutral is 38v in a panel board . whats the root cause.
Explain in details how you would react to an unexpected incident when your supervisor or manager is not around to give instructions?
when a cunductor is being disconnected from live cct, still it showing charged, if its checked by line tester?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)