Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is difference between Dy11 & Dyn11 vector group
transformer. Can both these transformers operate in
parrallel.

Answers were Sorted based on User's Feedback



What is difference between Dy11 & Dyn11 vector group transformer. Can both these transformers ..

Answer / ravi

Winding connection designations

High Voltage Always capital letters
Delta - D
Star - S
Interconnected star - Z
Neutral brought out - N

Low voltage Always small letters
Delta - d
Star - s
Interconnected star - z
Neutral brought out - n


Phase displacement
Phase rotation is always anti-clockwise. (international
adopted convention)
Use the hour indicator as the indicating phase displacement
angle. Because there are 12 hours on a clock, and a circle
consists out of 360°, each hour represents 30°.
Thus 1 = 30°, 2 = 60°, 3 = 90°, 6 = 180° and 12 = 0° or
360°.
The minute hand is set on 12 o'clock and replaces the line
to neutral voltage (sometimes imaginary) of the HV winding.
This position is always the reference point.
Because rotation is anti-clockwise, 1 = 30° lagging (LV
lags HV with 30°)and 11 = 330° lagging or 30° leading (LV
leads HV with 30°)



To summarise:
Dd0
Delta connected HV winding, delta connected LV winding, no
phase shift between HV and LV.
Dyn11
Delta connected HV winding, star connected LV winding with
neutral brought out, LV is leading HV with 30°
YNd5
Star connected HV winding with neutral brought out, delta
connected LV winding, LV lags HV with 150°


" So there is no specification of Dy11.. it will be Dyn11 "

Is This Answer Correct ?    63 Yes 18 No

What is difference between Dy11 & Dyn11 vector group transformer. Can both these transformers ..

Answer / pb

Dyn11 means Primary---Delta, Secondary---Star with neutral
brought out and secondary leading the primary by 30 deg

In case of Dy11 --- neutral is not brought out, rest
remaining the same as above.

Is This Answer Correct ?    28 Yes 6 No

What is difference between Dy11 & Dyn11 vector group transformer. Can both these transformers ..

Answer / sunny

thanks ravi
i had searched all over the net but didn't cleared myself.....
very easy & understanding

Is This Answer Correct ?    13 Yes 7 No

What is difference between Dy11 & Dyn11 vector group transformer. Can both these transformers ..

Answer / jim kirk

Mr Ravi

An excellent explanation - but there are DY11 transformers - we have two of them onsite

Is This Answer Correct ?    0 Yes 0 No

What is difference between Dy11 & Dyn11 vector group transformer. Can both these transformers ..

Answer / kandavel .p

Thanks Mr Ravi i understood clearly ,your way of explanation is good thanks lot

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

What are the basic & Majour problems in UPS ?

0 Answers   Roto Power, RotoPower,


why we need of power factor correction? give advantages

3 Answers  


What is DC power factor??

2 Answers   HCL,


how can we know the size of cable cross-section from current rating ?

3 Answers  


if we apply 1000ADC instead of 100ADC or We apply 50ADC instead of 100ADC,What will be happened in the test result value.Pl explain

0 Answers   NCC,


what will be d.g. capacity to cater together for 14hp A.C. load & 3kw lighting load

0 Answers  


what is the purpose of the armored for the power Or control cable? How to select the type of the armored?

1 Answers   Siemens,


please let me know , we have installed two separate motor for fire fighting system 1) 60 hp and 2) 15 hp the load is 74 AMPS and 20 AMPS then tell me the main power cable in Aluminum will be what thickness , the length is 225 mt from the main utility to fire pump house

1 Answers  


How can I model an open-delta ground transformer for a network supplied by 4 unit GTG and power transformer in ETAP?

0 Answers  


if voltage bt phase & nutral is 38v in a panel board . whats the root cause.

0 Answers  


Explain in details how you would react to an unexpected incident when your supervisor or manager is not around to give instructions?

1 Answers  


when a cunductor is being disconnected from live cct, still it showing charged, if its checked by line tester?

8 Answers   GEB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)