What will be happend if we not ground CT secondary?
Answers were Sorted based on User's Feedback
If the secondary of the CT is not grounded or short circuited
then the secondary current will become zero hence the ampere
turns produced by secondary will oppose the ampere turns of
primary(i.e brings to zero). So, there is no counter m.m.f so
high flux is produced in the core thus overheating of core is
produced. Similarly high e.m.f will be produced both in
primary and secondary this will damage the insulation of
winding. Thus for safe operation for the operator the
secondary must be grounded properly
Is This Answer Correct ? | 11 Yes | 2 No |
One terminal of secondary of CT is earthed to remove the
influence of high voltage of primary on secondary due to
inherent capacitance between them .
Is This Answer Correct ? | 3 Yes | 1 No |
In case of 3 phase motor why it is called single phasing by failure of one phare unless there is rest two phase are acting. ?
What will happen if we give transformer a dc not ac
What is the secondry voltage of 420kV Current Transformer , the rated current is 2600A
What is The Resistance Formula
I Need standard operation procedure(SOP)for 500kva Oil type transformer oil filtration & Procedure for IR value checking.
Why inductor short on dc and capacitor allow to flow ac?
In TNC switch, is there any 1NO+1NC block ? and if we move over closing position, is ther any affect on trip position or vice versa?
Why does not AC excitation use in rotor of AC Generator instead of DC excitation?
what is RFCT and Insulgard Relay & It's function?
how the 3phase induction motor is running in 2phase supply with help of capacitor?
What is bus-bar?
Why r used of cable 50sq.mm and above size cable in 3.5 core. And below size in 4 core ? any technical reason please explain it