how to size a diesel generator set?
Answer / mahesh sali
mostly total electrical cal.in KW at 0.8 pf as per thumb
rule.
KVA = KW/PF
as per nec code norms ur dg set shall be suitable to take
the higher inrush current during starting.
so awalys keep some say 115% to 125 % on induction motor
load.
for ups & lighting system around 200 to 300 %
Toatl kw rating = 1.25 * Kw ( Plant load )
KVA at 0.8 pf = Total kw/0.8
Assume that Dg set loading at 70%
i.e rated KVA = KVA /0.7
adding some 20% future load
i.e. actual DG ser rating in KVA = rated KVA + rated KVA *
20%
Thanks
Is This Answer Correct ? | 1 Yes | 0 No |
State the difference between Three winding transformers and Two winding transformers ? where its used?
how to check regenerative load in drived motor
0 Answers Hindustan Unilever Limited, NHPC,
UPS battery Back time = no.of Batteries * Ah of the Battery / output KVA * 130 ? what is the 130 means ? can any one help? because all are using this formula how its came 130?
Dear All, Can anybody please tell me which value(saturated or unsaturated) of sub-transient reactance(Xd") we take for the calculation of fault current of the system?
name the famous power plants in ap and vwhere it is located with capacity details
when motor taking high amp what happen.
What do you mean by a voltage transformer?
what is ideal insulator. what are its parameter. Is poecelain insulator comes under this category.
tube light how its working.,?
how to select a capacitor, i mean we use 3.5 mico ferad cap for a celling fan,but how to select a cap for 1h.p motor,etc.........
On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall be the current rating of DC MCB ?
6 Answers RR, TNEB Tamil Nadu Electricity Board,
Dear Sirs, I am a technical persons.In one of our Electrical Sub- Station, We have installed three numbers of 1250KVA ,11KV/0.415KV Transformer to feed the Factory load. We have found some abnormality. In one of our Transformers the leakeage current from transformer body to earth through earth continuity wire is almost 86 Amp but in other transformer it is (5-10)Amp. where the load current on three phase and neutral are respectively 1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical person help me about the reasons of this situation and how I can rectify the fault. Moreover,I have measured the earth resistance of the Earth continuity wire which is less than 1 Ohm. Thanks Tapas Barua