our company have 750 kva oil transformer.still we have
facing a problem that is when voltage is 11.5 kv coming
from HT side then LT-side voltage is 420v or above at tape
1.please give me best solution to decrease the voltage
Answers were Sorted based on User's Feedback
Answer / sudhakar lanka
my friend, you r looking for reduce the output voltage from 420 volts,
case1: try to keep the primary tap position on maximum voltage
for example ur receiving 11.5kv , if in your transformer there is a tap voltage which is more than these value i.e 11.6kv or else apply 11.5kv on that tap position.
same as above u can try on secondary side also
case2: if u have done all the these exercise, then when u connected to load on transformer there will be voltage drop
check at that time may be ur required voltage i.e rated voltage on motor or machine when it is running on load
other wise u can check with grid supply or substation to get required voltage
Is This Answer Correct ? | 4 Yes | 0 No |
Both the voltages are 5 % higher than the normal voltages ,that means tap position is for normal primary voltage . Check the name plate details
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
From the data furnished by you ,it appears that Tap No.1 is
the normal position as there is 5% rise in both primary and
sec voltages, for 11KV/400V Tr
Is This Answer Correct ? | 0 Yes | 1 No |
what effect on electrical equipment if PF is gone over 0.996 in leading when provider say that its keep in minimum 0.996lagging
define excitaton voltage and excitation current?
what is the current generated in a 230v megger?
what is green house effect?
When we need start the motor by method of star delta which size (KW or HP)motor should must be operate in Star Delta Method,
DERIVE AN EXPREION FOR MAXIMUM POER TRANSMISSION, WHAT ARE ITS APPLICATIONS.
what is the synchronous timer ? and it applications.
what is the question paper model for section engineer in RRB
how many typetesting of transformers?
Formula to calculate fault current flowing in the neutral line?
How much energy save vfd if motor run on 50 Hz (full speed)
what is megar testing