725KW Three DG set Synchronised but DG no-1 power showing
750KW DG n0-2 power showing 500KW DG no-03 showing 500KW.
DG is Shynchronised but why this different power showing?
Answers were Sorted based on User's Feedback
Answer / jince
Regarding paralleling DG sets we sticks only on the theoratical conditions of same voltage frequency phase angle and phase sequence. And now a days its easy to achieve using sync relays. Load sharing is the major thing in paralleling the DG sets. Many factors are depending on it
1. Droop of individual DG set must be same
Droop implies both voltage and frequency droop. it is the percentage of noload voltage or frequency. ex. 1% 2% 3% etc. Ex.1% voltage droop of 420V(noload)is 4.2V and it means on full load DG voltage comes down to 415.8V and not any more
Same is the case with frequency droop. All DG's droop must be same
2. On loadsharing we adjust voltage of DG's to met REACTIVE POWER AND SPEED(FREQUENCY) TO SHARE ACTIVE POWER
In order to share the load evenly we must control the voltage and frequency of individual DG's constantly
And it depends on load nature
In my personal experience for resistive loads (lamps)
loadsharing is not required as no variation occurs
For varying loads like lifts motors ac chillers compressssors etc constant loiadsharing is required
For clarification please reply
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tango
synchronization is basically done with Voltage, Frequency and Phase angle but It is recommended to Have same Power Rating of Transformer or DG, in your case it seems to be using DG's of Different rating and so they have been showing Power as per their capacity
Is This Answer Correct ? | 2 Yes | 2 No |
What is time response of the control system?
what is REF relay?
MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III
while starting a liquid starter ,is there any volage drop on water/soda on tank.can we touch the tank on starting?
what is different between electrical ckt&electronic ckt
What is your favorite aspect of the engineering field?
how to calculate diesel consumption of diesel generator by considering load and capacity of generator?
working method of railway electricl loco in single wire 25000 volt
I am a electrical engg. diploma holder,applied for junior engineer (electrical),Kolkata RRB. Have I to attend all electrical,mechanical&civil portion in written exam.???
What is the difference between Droop vs Isoch Control?
Why does the phase voltage of two healthy phases become equal to the line voltage in case of an ungrounded neutral 3 phase star connected sytem when a single line to ground fault occurs ?
in domestic service connection,what is service main?