Answer / jince

Regarding paralleling DG sets we sticks only on the theoratical conditions of same voltage frequency phase angle and phase sequence. And now a days its easy to achieve using sync relays. Load sharing is the major thing in paralleling the DG sets. Many factors are depending on it
1. Droop of individual DG set must be same
Droop implies both voltage and frequency droop. it is the percentage of noload voltage or frequency. ex. 1% 2% 3% etc. Ex.1% voltage droop of 420V(noload)is 4.2V and it means on full load DG voltage comes down to 415.8V and not any more
Same is the case with frequency droop. All DG's droop must be same

2. On loadsharing we adjust voltage of DG's to met REACTIVE POWER AND SPEED(FREQUENCY) TO SHARE ACTIVE POWER

In order to share the load evenly we must control the voltage and frequency of individual DG's constantly

And it depends on load nature
In my personal experience for resistive loads (lamps)
loadsharing is not required as no variation occurs

For varying loads like lifts motors ac chillers compressssors etc constant loiadsharing is required


For clarification please reply

Is This Answer Correct ?    3 Yes 0 No

725KW Three DG set Synchronised but DG no-1 power showing 750KW DG n0-2 power showing 500KW DG no-..

Answer / tango

synchronization is basically done with Voltage, Frequency and Phase angle but It is recommended to Have same Power Rating of Transformer or DG, in your case it seems to be using DG's of Different rating and so they have been showing Power as per their capacity

Is This Answer Correct ?    2 Yes 2 No

725KW Three DG set Synchronised but DG no-1 power showing 750KW DG n0-2 power showing 500KW DG no-..

Answer / kj

If the DG's are the same rating then the load sharing is
out of adjustment.

Load sharing can be by speed droop (see answer above) or by
load sharing controller.

Adjustment of either of these can rectify problem.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What is time response of the control system?

0 Answers  


what is REF relay?

1 Answers  


MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III

1 Answers  


while starting a liquid starter ,is there any volage drop on water/soda on tank.can we touch the tank on starting?

0 Answers  


what is different between electrical ckt&electronic ckt

4 Answers   Ashok Leyland,






What is your favorite aspect of the engineering field?

1 Answers  


how to calculate diesel consumption of diesel generator by considering load and capacity of generator?

1 Answers  


working method of railway electricl loco in single wire 25000 volt

1 Answers  


I am a electrical engg. diploma holder,applied for junior engineer (electrical),Kolkata RRB. Have I to attend all electrical,mechanical&civil portion in written exam.???

0 Answers   RRB,


What is the difference between Droop vs Isoch Control?

0 Answers  


Why does the phase voltage of two healthy phases become equal to the line voltage in case of an ungrounded neutral 3 phase star connected sytem when a single line to ground fault occurs ?

2 Answers  


in domestic service connection,what is service main?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)