Sir we have 12.5 MVA(110/11KV) transformer (Y-Y)
connected,which tripped showing earth fault,when we charged
transformer it stood OK ,but on connecting 11 KV feeders it
tripped showing earth fault.our service engineers found that
the B phase and R phase phase connecting to neutral broken
from HV OLTC(on load tap changer),and R phase and Neutral is
ok.Dissolved gas analysis shows that accetline content is
high,tan delta value is 12.My dout is it is an internal
fault of transformer,why REF or diffrential relay is not
acted?
Answer / k.prakashchandra
REF relay does not act as the unbalanced current is equal to
NCT current in all respects. And for diff relay, it also
does not act as the corresponding ct currents in HT and
sides for each phase are equal.If there is current in only
one phase ,EFR will trip as current's return path is through
the EFR.But why there is current in the single good phase as
all dist Trs are delta/ star connected ? May be due to star
connected line capacitors or dist trs/loads are also star
connected with neutrals earthed.
Is This Answer Correct ? | 0 Yes | 0 No |
We have two 1 phase heating coils having same resistance of 25ohm, but during operation one takes 3A and other 6A Is it posiible Pls. explain
why single core HT cable need only one side earthing?
When semiconductor fuse does save thyristor in each cycle of conduction? Why under voltage setting keep less in SPRS and more in DC drive?
How to take Vector group test of Transformer?
16 Answers Sunflag Steel, Zuari Cements,
1) Can anyone give me a typical value for Insulation Resistance of 11kV xlpe cable? 2) How much will the IR value decrease per KM of cable length added?
if we convert watt into kva,which one formula use by us,pls tell me?
what is pressure relief valve in D.G ?state its function?
what do you mean by linear and bilateral network?
why wound rotor is star-connected?
Can any body tell me what is use of END OF LINE RESISTOR in fire alaram circuit?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
Why in India distribution transformer are connected in Dyn11 when we know capacity of v-v connection can be increased by adding only a single transformer?