iam interesting to design the control panel for 3 phase
pump motors by controling single phase switches.iam plan to
use fuse,contactor & relay for motor protection .how can i
select the voltage & amps rating for fuse,contactor & relay
plz guide me .if anybody clarify my doubt means it will
more helpful for my future .
Answer / kuldeep singh
Fuse should be 2.0-2.5 times of full load current,
Contactor shall be 2.o times of fullload cureent ( with
AC23 duty) ,relay should be such that full load current of
motors is in mid the range of relay settings,
Isolater rating shall be 2.5 times of full load current
use 4 Amp fuse for your control circuit and aux contactor
of 2no + 2 nc contact etc
for more ask
kuldeepuee@rediffmail.com
KULDEEP SINGH
B.TECH
IITR
Is This Answer Correct ? | 0 Yes | 1 No |
what is subtransient , transient and study state ac components
what is the criterion for selecting vector group of Transformers ? i mean how to decide vector group of Generator transformer, substation trasformer and transformer at consumer end
1.where in India the maximum transmission voltage is operated? 2.what the methods are used to cool down the transformer?give the specific ratings of the transformer & specific cooling process. 3.how zero & negative sequence reactances are formed in a rotating machine when fault occur in the system?
if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?
How to find synchronous motor speed formula Ns=120f/P ?....
What is the following which is printed on electrical appratuses like AC21 ,AC 23 , etc ?
An engineer measures the direct current resistance of a transformer using ohm meter. When he/she takes out one of the leads of the meter, spark comes.. Why ?? This effect is known as...
what is the meaning of knee point in current transformer and how to calculate?
what is the difference between LT & HT Motors
How we calculat the NGR of 3phase Generator, Our generation voltage 11KV
how calculate external illumintion in a compound area. for e.g. there is one open park having 600m2 area and i have to put 40w flouresent tube fitting with pole. how shall i calculate the numbers of fitting.
what is the earth resistance