iam interesting to design the control panel for 3 phase
pump motors by controling single phase switches.iam plan to
use fuse,contactor & relay for motor protection .how can i
select the voltage & amps rating for fuse,contactor & relay
plz guide me .if anybody clarify my doubt means it will
more helpful for my future .



iam interesting to design the control panel for 3 phase pump motors by controling single phase swi..

Answer / kuldeep singh

Fuse should be 2.0-2.5 times of full load current,
Contactor shall be 2.o times of fullload cureent ( with
AC23 duty) ,relay should be such that full load current of
motors is in mid the range of relay settings,

Isolater rating shall be 2.5 times of full load current

use 4 Amp fuse for your control circuit and aux contactor
of 2no + 2 nc contact etc

for more ask

kuldeepuee@rediffmail.com

KULDEEP SINGH
B.TECH
IITR

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is subtransient , transient and study state ac components

2 Answers  


what is the criterion for selecting vector group of Transformers ? i mean how to decide vector group of Generator transformer, substation trasformer and transformer at consumer end

0 Answers   Areva,


1.where in India the maximum transmission voltage is operated? 2.what the methods are used to cool down the transformer?give the specific ratings of the transformer & specific cooling process. 3.how zero & negative sequence reactances are formed in a rotating machine when fault occur in the system?

2 Answers   IES,


if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?

3 Answers  


How to find synchronous motor speed formula Ns=120f/P ?....

2 Answers   Cranedge,






What is the following which is printed on electrical appratuses like AC21 ,AC 23 , etc ?

1 Answers  


An engineer measures the direct current resistance of a transformer using ohm meter. When he/she takes out one of the leads of the meter, spark comes.. Why ?? This effect is known as...

1 Answers   Saint Gobain,


what is the meaning of knee point in current transformer and how to calculate?

2 Answers  


what is the difference between LT & HT Motors

11 Answers   L&T,


How we calculat the NGR of 3phase Generator, Our generation voltage 11KV

0 Answers   MSP, Toyo Denki,


how calculate external illumintion in a compound area. for e.g. there is one open park having 600m2 area and i have to put 40w flouresent tube fitting with pole. how shall i calculate the numbers of fitting.

1 Answers  


what is the earth resistance

4 Answers   Micron Electricals,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)