I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION.
THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO
A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME
TIME IT IS STABLE.
WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY.
WHERE AS INDICATION FLUCTUATES.
WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE
FIELD IT INDICATION IS STABLE.
WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE.
PLEASE CLARIFY.

Answers were Sorted based on User's Feedback



I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS ..

Answer / aftab ahmed mazari

I agree with Mr. Satyendra Bhai Patel suggestions.
More over please check followings:
1. May be some electric motor starts and its cable routing
is near to your extension cable.
2. Also get check thermocouple,some time,its hot juction
got open and close with the passage of time. Replace
thermocouple.
3. Check loose connections.
4. Check thermocouple any wire being grounded at some time.
5. Any how, do not megger thermocouple extension wire.
Check it with normal multimeter.
aftabmazari@yahoo.com

Is This Answer Correct ?    6 Yes 0 No

I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS ..

Answer / satyendra bhai patel

check cable is screened or not ? i think this type of
problem occures when a little bit induction in wire .so
just screen your cable in indicator s terminal.problem will
be solved .
For more details u can contact me on 9005091827

Is This Answer Correct ?    2 Yes 0 No

I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS ..

Answer / rana mujahid

I agree with all above answers but I think the most chances
are may be TC hot junction is some time going to open and
close..........need to replace TC

Is This Answer Correct ?    1 Yes 1 No

I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS ..

Answer / sreedhar

Just Replace T/C

Is This Answer Correct ?    0 Yes 0 No

I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS ..

Answer / abhishek

please check instrument cables are earthen or not with
screened cables.this things only happens when wires are cut
at gland side or terminations are loosed

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

modbus and profibus communication difference?

1 Answers  


What should be the stanchan Height for installation of Smoke detector & toxic gas detector in field,according to qatar standard

2 Answers  


What is the function of SMPS

2 Answers  


HELLO FRENDS ,, I M IN THE MIDST OF TROUBLE .. JUST LITTLE HELP ME... SUPPOSE ,, I HAVE A CLOSE VESSELE TANK ( HEXANE MEDIA ) ,, I M USING ROSEMOUNT 2051 DPT FOR LEVEL APPLICATION .. ITS CALIBRATE RANGE IS.. . 0 TO 950 MMH20 ..I DID CALIBRATED DPT WITHOUT REMOVING IMPULSE LINE OF HIGH AND LOW TAPPING.. & WITHOUT DISTURB 3 WAY MANIFOLD..!!! BUT ,,, DURING CALIBRATION I SELECT RANGE BY HART LRV IS 900 MMH20 & URV IS 1300 MMH20 ,, BUT ,TANK LEVEL SOMETIMES 100 % AT 1100 MMH20 , SOMETIMES 1300 MMH20 ..IN THIS CONDITION .. WHOLE LOOP FAILED ,, MAIN THING IS THAT ,, HOW TO CUSTOME RANGE SELECT ?? AND IF I USED RANGE OVER THE ORIGINAL CALIBRATE RANGE ,,,THEN WHAT ERROR WILL BE COME ??? HOW TO ZERO CALIBRATION OF DPT... HOW TO ZERO TRIM BY MANIFOLD ?? AND FOR TANK LEVEL PURPOSE ... WHICH UNIT I CAN USE ??? IS THERE ANY CALCULATION OR CALIBRATION .. IF YEH .. THEN PLZ JUST GIVE ME CALIBRATION STEPS FOR DPT.. THANKS YOURSSSSSSS

1 Answers   Torrent Pharma,


what is positive feedback and negative feedback?

2 Answers   CEPC,






Somebody can explain me about >Critical Loops, calibrations, ESD critical Loop checks, Logic Diagram / Cause & Effect checks for ESD loops,

0 Answers  


is fan is a transducer or inverse transducer?

5 Answers  


The Design Calculation of Level Transmitter For Different Structure open & Closed Vessel, Eg. Diff. Level Tx., Capacitance For Continous Operation

0 Answers   Reliance,


how do we commission inergen system?

0 Answers  


When a timer is placed in RS Logix 5000 with preset value less than its scan time it is malfunctioning. i.e., if the preset is set to 30ms still the timer TT bit is counting till 150ms(its scan time). Any solution for the problem?

2 Answers   Balco,


send me last 5 years questions asked in rrb chennai, for section engineer

0 Answers   RRB,


what is maximum vaccume?

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)