I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION.
THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO
A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME
TIME IT IS STABLE.
WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY.
WHERE AS INDICATION FLUCTUATES.
WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE
FIELD IT INDICATION IS STABLE.
WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE.
PLEASE CLARIFY.
Answers were Sorted based on User's Feedback
I agree with Mr. Satyendra Bhai Patel suggestions.
More over please check followings:
1. May be some electric motor starts and its cable routing
is near to your extension cable.
2. Also get check thermocouple,some time,its hot juction
got open and close with the passage of time. Replace
thermocouple.
3. Check loose connections.
4. Check thermocouple any wire being grounded at some time.
5. Any how, do not megger thermocouple extension wire.
Check it with normal multimeter.
aftabmazari@yahoo.com
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / satyendra bhai patel
check cable is screened or not ? i think this type of
problem occures when a little bit induction in wire .so
just screen your cable in indicator s terminal.problem will
be solved .
For more details u can contact me on 9005091827
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rana mujahid
I agree with all above answers but I think the most chances
are may be TC hot junction is some time going to open and
close..........need to replace TC
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / abhishek
please check instrument cables are earthen or not with
screened cables.this things only happens when wires are cut
at gland side or terminations are loosed
Is This Answer Correct ? | 0 Yes | 1 No |
modbus and profibus communication difference?
What should be the stanchan Height for installation of Smoke detector & toxic gas detector in field,according to qatar standard
What is the function of SMPS
HELLO FRENDS ,, I M IN THE MIDST OF TROUBLE .. JUST LITTLE HELP ME... SUPPOSE ,, I HAVE A CLOSE VESSELE TANK ( HEXANE MEDIA ) ,, I M USING ROSEMOUNT 2051 DPT FOR LEVEL APPLICATION .. ITS CALIBRATE RANGE IS.. . 0 TO 950 MMH20 ..I DID CALIBRATED DPT WITHOUT REMOVING IMPULSE LINE OF HIGH AND LOW TAPPING.. & WITHOUT DISTURB 3 WAY MANIFOLD..!!! BUT ,,, DURING CALIBRATION I SELECT RANGE BY HART LRV IS 900 MMH20 & URV IS 1300 MMH20 ,, BUT ,TANK LEVEL SOMETIMES 100 % AT 1100 MMH20 , SOMETIMES 1300 MMH20 ..IN THIS CONDITION .. WHOLE LOOP FAILED ,, MAIN THING IS THAT ,, HOW TO CUSTOME RANGE SELECT ?? AND IF I USED RANGE OVER THE ORIGINAL CALIBRATE RANGE ,,,THEN WHAT ERROR WILL BE COME ??? HOW TO ZERO CALIBRATION OF DPT... HOW TO ZERO TRIM BY MANIFOLD ?? AND FOR TANK LEVEL PURPOSE ... WHICH UNIT I CAN USE ??? IS THERE ANY CALCULATION OR CALIBRATION .. IF YEH .. THEN PLZ JUST GIVE ME CALIBRATION STEPS FOR DPT.. THANKS YOURSSSSSSS
what is positive feedback and negative feedback?
Somebody can explain me about >Critical Loops, calibrations, ESD critical Loop checks, Logic Diagram / Cause & Effect checks for ESD loops,
is fan is a transducer or inverse transducer?
The Design Calculation of Level Transmitter For Different Structure open & Closed Vessel, Eg. Diff. Level Tx., Capacitance For Continous Operation
how do we commission inergen system?
When a timer is placed in RS Logix 5000 with preset value less than its scan time it is malfunctioning. i.e., if the preset is set to 30ms still the timer TT bit is counting till 150ms(its scan time). Any solution for the problem?
send me last 5 years questions asked in rrb chennai, for section engineer
what is maximum vaccume?