What is minimum distance between three thermocouples (2oo3)
mounted on same pipe line (20")?
Technically accepted by stright line mounted or circler
mounted?
Answer / rajkumar
120 degrees in the same plane (circular), especially if
there has not been sufficient thermal mixing of the process
at the point of measurement. In this case, the average of
the temps should be used for control (as opposed to the
middle of 3) in addition to any deviation checking used to
detect a failed TC.
If any thermal streaming is occurring, then mounting the TCs
linearily down the pipeline reduces your chances of
measuring it.
| Is This Answer Correct ? | 3 Yes | 3 No |
which type inter lock use in petrochemical refinery,and oil & gas?
HOW TO CHECK THERMOCOUPLE AND RTD & WHAT IS THE DIFFERENCE BETWEEN THERMOCOUPLE AND RTD
what are the different types of Protocols? & their applications.
6 Answers Infosys, Sitara Chemical Industries, Syntel, VSNL,
where proximity sensor installed on tank in loading arm application
what is ment by PID controllers? explain with example?
what is the difference between hub and switch?
Explain the working principle of lvdt?
deference between DCS and PLC including date processing and architacture.
How to calibrate capillary type level transmitter
A pressure Tx accuracy is 0.2%. Signal o/p is 4-20ma.span is 16 Ma.how many deviate the o/p then calibration needed
WHAT DO WE MEANT BY INSTRUMENT MAINTENANCE IN SOFTWARE SIDE.
please explain smoke detectore & lel detector?what is o/p
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)