What is minimum distance between three thermocouples (2oo3)
mounted on same pipe line (20")?
Technically accepted by stright line mounted or circler
mounted?
Answer / rajkumar
120 degrees in the same plane (circular), especially if
there has not been sufficient thermal mixing of the process
at the point of measurement. In this case, the average of
the temps should be used for control (as opposed to the
middle of 3) in addition to any deviation checking used to
detect a failed TC.
If any thermal streaming is occurring, then mounting the TCs
linearily down the pipeline reduces your chances of
measuring it.
Is This Answer Correct ? | 3 Yes | 3 No |
What is the main difference between the terms instrumentation and Automation?
Explain PID controller tuning & any one method used for it.
what is commissioning & pre commissioning , explain with difination
2 Answers Bapco Bahrain Petroleum Company, Shell,
How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error
what is dedband in instrumentation ?
What is mean by Adapter block and net block?
3. Differentiate between ultrasonic flowmeter and radar type flow meter.
Can we used Condensate Pot on flow transmitter which is using on liquid having sluge and DP transmitter is in pit and below the process line,Can we used Condensate pot for accamulate the Sluge?
what do you mean by smart instruments ? define ? give an example?
2 Answers Flour Tech Engineers (P) Ltd,
defination of plc
what is surge and how is it prevented, what is the purpose of bypass valve across AS valve.
How to erection of DCS Panel at site step by step