can we replace a pressure transmitter of range 0 to 25
Kg/cm2 by a Pressure transmitter of range 0 to 10
Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we
will feed to the PLC.
Answers were Sorted based on User's Feedback
Answer / ruchita
Yes it will affect the 4-20 mA signal. say for example if we are using PT of rsnge 0 to 25 bar bt internally we use only 0 to 10 bar range den it can be replaced otherwise not
Is This Answer Correct ? | 9 Yes | 4 No |
Answer / yashwant
yes, only make sure the pressure will never rise beyond 10 I
think its design for 25 in safety condition. if u wish O/p in
0-10 you can scale 4-20 ma as 0-10 at plc, no need to change
tx.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / vijay
it depend upon ur range in the application for example
piston producing pressure within 10kg/cm2 then u can use it
by change program in the plc otherwise u cant
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / vinod hepat
Yes first of all note whether range is suitable for ur
application.replace transmitter & accordingly change the
range in DCS.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / madhav kamble
Yes. you can replace the pressure transmitter form 0-25 to
0-10. it willnot change the 4-20 mA which we will send to
the PLC but you to change the calibration at PLC for New
0-10 transmitter.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / govind singh
Going by standards, 20 mA of first transmitter will read 25 kg/cm2 pressure, while same reading for second transmitter will be 10 kg/cm2. So at same pressure, both transmitters will send different current signals. So calibration at the DCS end will be needed.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / imran
first of all you need permission to replace pressure tx
from operation instead 0-25 by swaping 0-10cause it will
effect process & may you r going to upset process other
point of view by technical you need to configure it & it
will give you output vice varsa
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / dinesh kumar
Its not possible by answering without knowing the application
But in both the cases v can get the 4-20mA output
In case if the o/p doesnt goes beyond 10kg then v can replace and the o/p side of tx shud be calibrated before installing and the changes shud be entered on plc.
In another case if the user wants better accuracy he may b using 0-25kg/cm2 tx eventhough the internal pressure is b/w 0-10kg/cm2
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / trideep
If range is in b/w 0-10 kg/cm2 or with in that, then it will do..
Is This Answer Correct ? | 0 Yes | 3 No |
i have 80cm water tank.how can i use DPT as level mesurment.pls give specs for that..? We have air comp.from that moisture comeout to one tank.i want to mesure level of water in that tank and then after operat one sov to dicharge water after high level.
Hi,can anyone help me out with PhD programs related to Instrumentation field?I have a degree in electronic Instrumentation?
what is Mv with respect to temprature in thermocouple
can u guys tell me why we are using sheild in junction bos wiring ~! ?
IS THEIR ANY AGEING EFFECT ON FLOW NOZZLE, ORIFICE, MANIFOLD, OR TRANSMITTER ?
why to use 3 wire at RTD ? what's the reason for common wire ?
admittance level sensor meaning?
How Many Slave Can be used in one slave ?
what is protonics how it is differ from electronics
why are use only 4 to 20ma. signal.
meaning of SMART
what is the square root flow transmitter formulla ?