why we use 0.2 to 1.0 kg/cm2 output in control valve
Answers were Sorted based on User's Feedback
Answer / pankaj nandasana
As you know....0.2 to 1 kg/cm2 is equal to 3-15 psig..
Generally we are considering this range...reasons are following...
1) Suppose if your have set lower limit at 0 psig, then how you can differentiate zero signal level and pipe breakage..!!!! You can not distinguish two thing..That why we select some elevated range from 0 psig.
2) Our all instrument are producing linear response in the range of 3-15 psig.
3) Pneumatic supply to all instrument is 20 psig..so alway there is bleading of air from instrument..for standardlisation purpose all are considering 3-15 psig..
Is This Answer Correct ? | 33 Yes | 0 No |
Answer / ashish namdev, bina refinery [
The diaphragm design of all control valves are universal and
the out of the actuators are 3 to 15 psi.When more than the
15 psi pressure is acting to the diaphragm that will lead it
to faulty so we use the 0.2 to 1.0kg/cm2 for control valves.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s k
because the control valve work within the specified pressure
range of about 0.2 to 1.0 kg/cm2.
Is This Answer Correct ? | 2 Yes | 8 No |
What is difference between “Fault Tolerant” & “Fault avoidance” PLC? Application where these system s are used?
What is an SCR?
what is the reason for flow fluctuations happen on differential flow transmitter during in service
what is an ambient temperature?
anybody having Qatar Petroleum questions for instrument Technician offshore ....please send me
What is Vena contracta?
What are Sinking and Sourcing IO Cards
what is vfd(variable frequency drive)?type of vfd.
Please explain about FAT? What is the difference between FAT and SAT?
why ultra sonic level transmitter is installed in 90 degree?
How would i calibrate a new commissioned flow transmitter???
Dear friends, I have a question: We work on a project which has some boilers to provide steam for desalination unit. The boiler area is safe and the only hazard source is the fuel lines of boilers. I want to know according to NFPA standard which type of instrument should be selected on the fuel line: Eex Type or Non-Eex type? Thanks in advance