Answer / pankaj nandasana
As you know....0.2 to 1 kg/cm2 is equal to 3-15 psig..
Generally we are considering this range...reasons are following...
1) Suppose if your have set lower limit at 0 psig, then how you can differentiate zero signal level and pipe breakage..!!!! You can not distinguish two thing..That why we select some elevated range from 0 psig.
2) Our all instrument are producing linear response in the range of 3-15 psig.
3) Pneumatic supply to all instrument is 20 psig..so alway there is bleading of air from instrument..for standardlisation purpose all are considering 3-15 psig..
| Is This Answer Correct ? | 33 Yes | 0 No |
Answer / ashish namdev, bina refinery [
The diaphragm design of all control valves are universal and
the out of the actuators are 3 to 15 psi.When more than the
15 psi pressure is acting to the diaphragm that will lead it
to faulty so we use the 0.2 to 1.0kg/cm2 for control valves.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s k
because the control valve work within the specified pressure
range of about 0.2 to 1.0 kg/cm2.
| Is This Answer Correct ? | 2 Yes | 8 No |
To find closed tank level by DP transmitter , how to findout its range.and insomeplace they using range like - 1500 to +1500 mmwc why not 0 to 3000 mmwc. how they spilit they range for minus and plus.and why?
What is inside the PLC panel? How does instruments communicate to DCS computer via PLC? What is the type of wiring in PLC connections? Please answer... Thanks
in my plant 100% feedwater control v/v is air to close but due to instrument air fail,the valve opens but instead of drum level high its get tripped in low low drum level.the urv of level tx is 0 and lrv is -800.pls tell me the reason. for such behaviour.
How to carry out hot loop checking of closed loop pf temperature control valve & temperature transmitter?
what is droop mode n frequency mode in wood ward governor?
why? Boiler furnesh pressure transmitter mount in boiler top and it's impulse line is in bottom of the boiler. Aneybody kindly tell me this reason.
can we control operation of PLC from operator station?
what r all the type of viberation measurement measuring in turbin? what's the output of viberation sensor?
Hi buddies! my name is sachin and i am working as a electrical and instrumentation engineer in a paper plant. right now i am facing a problem and if someone could help me it will be an immense pleasure to me. i am using AC 800M to synchronise DCS500 drives on paper machine and rewinder.communication is on PROFIBUS and we are using NPBA-01 module to link profibus to DC drives.But these days two of these drives are showing a error named FIELDBUS COMM.TIMED OUT and the drives get tripped.I have changed the NPBA module and PROFIBUS cable.So if anyone can do please help me out with this problem.I'll be highly grateful.
Explain the difference between differial pressure & delta pressure?
how magentic flow tx. vortex flow tx & ultrasonic flow tx works and its prinicle?its callibtration prosedure?
How to calibrate the magnetic flow meter and how to correct the flow if it is showing more flow.
5 Answers Bohra Industries Limited, TCL,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)