in transformers for ex. 100mva and 400kv the secondary
current is about 420 amps but for selection of bushing the
capacity of selected bushing is 2000A why there is such
big difference ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The insulated leads of secondary from the Tr windings are
taken through hollow rods inside the bushing and connected
at the top.As the rod has to bear the all the mechanical
forces like torsion and strain, the wall has to be thick enough.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / k.prakashchandra
I must have used the word 'pipe' instead of rod.Further,in
the condenser type bushing the oil inside is locked and
isolated from the oil in the tank.Hence it is deprived of
cooling. The pipe should be of much higher capacity to avoid
heating up due to the current flowing through it.
| Is This Answer Correct ? | 0 Yes | 2 No |
Why transformer rating in KVA? describe.
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
What is power in wattage of 8.5 TR AC
1. Can a 12v DC choke operate a 60v/12w PL lamp ? 2. Can a 230v ballast fire / operate a 60v/12w PL lamps.
0 Answers ICS Integrated Computer Solutions,
Why we use a H.T. Fuse from a thick wire, on other side we use high rating of cables? & Why we use less Sq. mm Cable on H.T. side , on other side we use Large Sq. mm cable?
how to revers the direction of single phase motor
What should be the Sandwitch type Al. bus bar capacity for 2 M.W.Gen. set, having continuous full load current- 3463 Amps,ambient temp.- 50 Deg. C., Required temp. raise-20 deg.C., it will run 24 hrs, 365 days on full load, required highly reliable.
What are the types of windings present in the ceiling fan? What winding will be effective first when we started the fan?What are the resistance and inductance ratios comparatively at the initial speed and full speed of the fan?
Usually in the L & T make MCC feeders' power circuit,we have BMR after the MAIN CONTACTOR.,can we interchange their position, keeping the control logic same???
can we run the home fan both clock and anticlockwise direction
How to select a contactor? How many types of contactors are available
How to select the cable size for the given load ?Pls explain the Formulae
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)