Answer / himanshu amin
dp trasmitter is having range of few w/c. take example of
you want to calibrate 0-50 in h2o dp transmitter. connect
power supply and multimeter to connection point. connect
small hand pump to high side of dp transmitter. keep low
side of dp open to atmosphere. first check 4ma when both
connection are open to atmosphere. then connect hand pump
to high side and give 12.5, 25.0,37.5 & 50 in h20 and check
8,12,16,&20 ma o/p.
| Is This Answer Correct ? | 8 Yes | 0 No |
what is HVAC?
what is intrinscily safe system and where we use?
What is the function of a diaphagram
how to measure the output of RTD given the general formula of rtd.
steam drum level transmitter calibration procedure? with example?
what's the minimum level required of SIL (safety integrity level)to use fire and gas system?
why we are using perforted cable tray for control cable and ladder tray for power cable
Why do we floating DC in DC system.
in any transimitter (flow/level) there are three terminals for supply& test (+,-,+)in two wire,24VDC given to Tx.,but how 4-20 ma signal travels thru same wire (as it is for 24VDC input supply)?
WHY RESISTANCE TEMPERATURE DETECTOR IS AN ACTIVE DEVICE
What are advantages and disadvantage of the ac supply load cell?
How is PH sensor works ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)