how to measure the output of RTD given the general formula of rtd.
Answers were Sorted based on User's Feedback
RTD's output is resistance.
As we know RTD means resistance temperature detector, so we measure resistance across the terminal of RTD by multimeter.
Now assume measured resistance is "X" and RTD we are using is PT100 then,
T(temp)=(X-100)/(0.386)
*PT100 RTD shows 100 ohm at 0°c
Is This Answer Correct ? | 17 Yes | 0 No |
Answer / rajesh.
RTD is Resistance Temperature Detector. As temperature varies resistance also change. So the output of RTD is Resistance. Which in terms converted into current (4 – 20 ma) by means of Transmitter. Generally RTD is available as Pt100.
Pt100 means 100OHMS at 0’ C for a platinum resistance bulb.
Formula for RTD:
Rt. =Ro (1+α t)
Rt. =Resistance of zero temperature.
α = Co. off of thermal (expansion)
t = temperature to be measured.
Example:
Calculation of Resistance or Pt 100.
Ro. = 100
α for platinum = 0.00385/c.
To calculate Resistance at 100’c
R100 =100(1+(38.5*104*100))
100+ (100*0.385)
R100 =138.5
Resistance at 100’c = 138.5
Is This Answer Correct ? | 4 Yes | 0 No |
Can a Differential Pressure Transmitter be used as a normal pressure transmitter??
why fuse block is not used for AI signal?
what is Dry Leg calibration and where is it used
kindly tell where orifice,nozzle,air foil,ventury used in flow measurement?
please tel me the calibration of pneumatic controler.
when the force applied on load cell the ohms will be varriying .and how its convert ohms to mv generate and have any formulae?
1 Answers UETCL Uganda Electricity Transmission Company Limited,
What is the use of double seated valve?
What is the formula To convert Degree centigrade to foranhight.
The Design Calculation of Level Transmitter For Different Structure open & Closed Vessel, Eg. Diff. Level Tx., Capacitance For Continous Operation
what is start up vent valve ? why it is used in boiler?
8 Answers ACC, Bhushan Power Steel,
Is an analogue only transmitter as accurate as a smart transmitter?
If you calibrate a pneumatic pressure transmitter, how many adjustments are normally necessary or mandatory?