what is difference between RCB,RCCB &RCBO?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
RCB- residual current breaker ,it is same as
RCCB.RCBO-residual current breaker overload (it protects
against overload also)
| Is This Answer Correct ? | 20 Yes | 7 No |
Answer / tushar kanti saha
RESIDUAL CIRCUIT BREAKER(RCB) IS SIMILAR TO RESIDUAL CURRENT CIRCUIT BREAKER(RCCB).
RCCB- IT PROTECTS THE CIRCUIT WITHOUT AN OVERLOAD.
BUT RESIDUAL CURRENT CIRCUIT BREAKER OVERLOAD(RCBO)- IT PROTECTS THE CIRCUIT WITH AN OVERLOAD, MAINLY WHERE WE NEED MORE EARTH LEAKAGE PROTECTION AT THERE RCBO IS USED.
| Is This Answer Correct ? | 15 Yes | 5 No |
Answer / ashmal zadir
RCD is the group name for residual current protective devices.
RCCB is an RCD that fits in the breaker panel
RCBO has additional overload protection and also fits in the breaker panel. RCBOs were mainly designed to protect individual circuits inplace of an MCB. RCCB is used to protect many circuits with individual MCBs
I assume RCB is just another name for RCD. Here is a good link where i found the information.
http://www.cycloflow.com/2014/02/what-are-elcb-rccb-rcbo-and-rcds.html
| Is This Answer Correct ? | 8 Yes | 0 No |
Explain marx circuit.
which will glow brighter?bulb 1 (110v,100w) and bulb 2 (230v.200w) series connection
what is the difference between core & shell type transformer ?& where we use those transformers ?
HOW DOES THE FAN REGULATOR CONTROLS ITS SPEED
WHAT ARE THE EFFECTS OF SERIES RESONANCE AND PARALLEL RESONANCE ON THE CIRCUITS PARAMETERS?
What is difference between Harmonic and Non harmonic Capacitor Bank?
from which formula we select a capacitor rating?
why we use 50 hz frequency in india .. why not 60 hz
What should be current in the Primary and secondary side of 1000KVA (11KV Supply)Transformer.?
What is YNyn Transformer? and what are the other types in this?
We have a bank capacitor rating of 60 KVAR for a overall load of 160 KVA and we have connected three loads of 50KVA each. We would like to auto matically correct PF using APFC. How do we design it?
Can HT cable(11kv cable) be used for 415V, 700A requirement.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)